when calculating the min csa of main earth using the adiabatic what current value do you guys use?

Do you measure the PFC and use that, or do you calculate using 230V / Ze, or do you use the tables in BS7671?

Been reading up on it, and seems a bit of grey area on here!

Also would you go with a 0.1 sec or 5sec disconnection time for a BS 1361 man fuse?

Thanks
 
i go by the pefc then get the dis. time from time/current tables.
 
Thanks Tel

so say you measure the PFC as 3.1KA and its a 1361 100A, I take it you would use a disconnection time of 0.1 as 1450A is the largest fault current listed?

Thanks
 
Hi,

when calculating the min csa of main earth using the adiabatic what current value do you guys use?

Do you measure the PFC and use that, or do you calculate using 230V / Ze, or do you use the tables in BS7671?

Been reading up on it, and seems a bit of grey area on here!

Also would you go with a 0.1 sec or 5sec disconnection time for a BS 1361 man fuse?

Thanks
If you've measured the actual Pfc then use that.
Where this fault current value intersects with the time on the time/curve graph in the book use that time in the adiabatic equation.
 
0.1 seconds is the lowest disconnection time the manufacturers will quote I believe.
 
Thanks Tel

so say you measure the PFC as 3.1KA and its a 1361 100A, I take it you would use a disconnection time of 0.1 as 1450A is the largest fault current listed?

Thanks

exactly that. don't forget that if it's a single earthing conductor ( not enclosed in a multicore cable ) the value for k is 143, not 115.
 
  • Like
Reactions: 1 person
so for example,

PFC 3.1KA measured

3100 x 3100 x 0.1 = 961000

square root = 980.306

980.306 / 143 = 6.85

and for a TT with 100A 1361, with a PFC of say 30A

30 x 30 x 1 (1 sec disconnection time) = 900

square root = 30

30 / 143 = 0.209

Obviously the PFC on the 2nd calc will not take out the main fuse, just want tomake sure I have got my theory right with regards to the adiabatic!

Thanks


 
looks OK.but don't forget with a TT system, the PEFC might be considerably higher than you calculate from the Ze, due to parallel paths ( bonding).
 
Yes, that's a thought, would you use the PEFC or The PSCC as the I value? Or the highest of the 2?
 
use pefc, as that's the fault current that the earthing conductor would carry.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
A little bit of clarity!
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
11

Thread Tags

Tags Tags
little

Advert

Thread statistics

Created
hoppy,
Last reply from
tony mc,
Replies
11
Views
1,789

Advert