H
hoppy
Hi,
when calculating the min csa of main earth using the adiabatic what current value do you guys use?
Do you measure the PFC and use that, or do you calculate using 230V / Ze, or do you use the tables in BS7671?
Been reading up on it, and seems a bit of grey area on here!
Also would you go with a 0.1 sec or 5sec disconnection time for a BS 1361 man fuse?
i go by the pefc then get the dis. time from time/current tables.
Thanks Tel
so say you measure the PFC as 3.1KA and its a 1361 100A, I take it you would use a disconnection time of 0.1 as 1450A is the largest fault current listed?
Hi,
If you've measured the actual Pfc then use that.
Where this fault current value intersects with the time on the time/curve graph in the book use that time in the adiabatic equation.
0.1 seconds is the lowest disconnection time the manufacturers will quote I believe.
Thanks Tel
exactly that. don't forget that if it's a single earthing conductor ( not enclosed in a multicore cable ) the value for k is 143, not 115.
Reactions: 1 person
so for example,
PFC 3.1KA measured
3100 x 3100 x 0.1 = 961000
square root = 980.306
980.306 / 143 = 6.85
and for a TT with 100A 1361, with a PFC of say 30A
30 x 30 x 1 (1 sec disconnection time) = 900
square root = 30
30 / 143 = 0.209
Obviously the PFC on the 2nd calc will not take out the main fuse, just want tomake sure I have got my theory right with regards to the adiabatic!
looks OK.but don't forget with a TT system, the PEFC might be considerably higher than you calculate from the Ze, due to parallel paths ( bonding).
Yes, that's a thought, would you use the PEFC or The PSCC as the I value? Or the highest of the 2?
use pefc, as that's the fault current that the earthing conductor would carry.
A little bit of clarity!
Thread Tags
Tags Tags
little
hoppy,
tony mc,