advice needed please if anyone can help I have a three phase generator on site that is going to power up one of our machines, the cables that are on it are L1,L2,L3 and earth there is a space for neutral but it hasn't been used, inside the electrical panel there is no destinct neutral or earth bar, also there is a neutral inside the panel connected to the same place as the incoming earth, there is a 230v socket on the side of the panel which I'm guessing needs the neutral but wounded that mean that the earth would have current passing through it, any idea the correct way this should be wired.

Thanks any help would be appreciated.
 
Don't know if these images would give anyone a better idea on what I'm talking about

IMG_3094.JPG


IMG_3095.JPG


IMG_3098.JPG
 
The earth and neutral are generally derived from the same point that being the star/wye connection of the generator windings, the neutral/earth point.
 
It looks like the Neutral is derived locally, but if the generator is adjacent to the incomer shown then this should be OK but the PEN conductor should be marked as such.
I would usually expect the Neutral and earth to be supplied at the generator the connection has been moved in your case to the main board.
Neutral and Earthing of local generator supply.gif
ESQCR regulations:
General requirements for connection with earth
8.—(1) ...
(2) ...
(3) A generator or distributor shall, in respect of any low voltage network which he owns or operates, ensure that—
(a) ...
(b) every supply neutral conductor is connected with earth at, or as near as is reasonably practicable to, the source of voltage except that where there is only one point in a network at which consumer’s installations are connected to a single source of voltage, that connection may be made at that point, or at another point nearer to the source of voltage; and
(c) ...
(4) A consumer shall not combine the neutral and protective functions in a single conductor in his consumer’s installation.
(5) Paragraphs (1) to (3) shall not apply to a network which is situated within a generating station if, and only if, adequate alternative arrangements are in place to prevent danger.
 
It looks like he has been doing something because one pic shows one neutral conductor at the rcd, another it has two. Same with the bar to the right, one pic nothing, another it has a cpc and neutral.
 

Reply to Advice needed please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
742
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
292
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
607
Hello. New member here. Electrical enthusiast. I am at a friend's house in the Bahamas and decided to look at the load center in the house, which...
Replies
2
Views
414
I’m just finishing my L2 2365 at college in the evenings and plan to do the L3 2365 with the same college as an evening course. However I would...
Replies
0
Views
250

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock