As I'm sure you are aware Amd 3 states that wiring in escape routes should have fire resistant supports.

Just wondering what others would do from a realistic and practical point of view if you were to add an additional light in a corridor say. Would you then have to ensure that all the wiring for that lighting circuit in the escape route had fire resisting supports.

Seems a bit impractical but just interested to know what other would do.
 
My understanding is that the the Whole of the circuit needs to comply even if I am only adding say 2 mtrs of twin and earth or am I mistaken. I hope so.
 
The modification you do must comply with the wiring regulations, this compliance may involve the rest of the circuit from say a consideration of Zs or the circuit protective device or if there is already a 6 A load on a 6 A circuit you cannot add more load. However there is no requirement to upgrade the rest of the circuit to full compliance, it must be safe to make your modification that is all.
Say you are adding a cable to a piece of PVC trunking across an escape route, then if you have the chance (and the approval of the customer) then you can support all the cables in that length trunking and not just your cable as this would probably be easier.
 
Many thanks Richard Burns for clarifying this. Is there anything in the regs that states that just your work needs to comply rather than the whole circuit or is it a case of interpretation?
 
From the index:

tmp_14900-DSC_0341-1176430658.jpg

:rolleyes2:
 
Cheers. So from section 610.4 my interpretation is that only the addition or alteration must comply not the rest of the circuit. Many thanks.
 

Reply to AMD 3 wiring in escape routes in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I have two questions regarding wiring and containment on commercial property stairwells in Ireland. We are currently wiring a 3 story...
Replies
10
Views
703
Hi. Looked at a job this morning for remedial work on an EICR. The inspection has noted the plastic consumer unit within the hallway cupboard and...
Replies
7
Views
2K
I have a job coming up where I likely need to replace old twin and earth (imperial size) feeding one, perhaps two flats in a 3 storey converted...
Replies
20
Views
2K
This weekend I was replacing a hall light fixture in my old home (rewired circa 1980/90's) and noticed the work was done using one of the exposed...
Replies
1
Views
1K
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
326

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock