Richard3009

Just trying to work out a cable and fuse size for a 3kva 415/240v transformer with a 2kW load on it, using Amtech single cable, there are no settings for showing a transformer on the load side, is it possible to calc a transformer load on Amtech.

If I use a motor as the load it chooses fuses very close to the load rating, but I'm sure the transformer inrush will rupture them. I can uprate the fuses but if I do that what's the point of using Amtech in the first place.
 
Do a calc for the TX load and then do a calc for the secondary load
 
Well it's bound to have a kva rating or should have
 
Should the primary fuses be inrush rated for 3kva + 10% and the secondary fuses rated for the load
 
What do you think?
 
If the TX has bee sized correctly, then size the protection on the secondary to suit the designed load.
 
Just trying to work out a cable and fuse size for a 3kva 415/240v transformer with a 2kW load on it, using Amtech single cable, there are no settings for showing a transformer on the load side, is it possible to calc a transformer load on Amtech.

If I use a motor as the load it chooses fuses very close to the load rating, but I'm sure the transformer inrush will rupture them. I can uprate the fuses but if I do that what's the point of using Amtech in the first place.
Is it 240V single phase?
 
Is it 240V single phase?


supply to the transformer is 2 wire 415v, output is 240v single phase yes, do you calc the cable based on a the kva rating of the transformer, could you just use a 3 phase motor to rate it on amtech
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Amtech 3 phase tx load
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
Richard3009,
Last reply from
Richard3009,
Replies
9
Views
3,582

Advert