I am still thinking of going down the supplementary rod road just incase the loss of a PEN conductor

Would TT not be safer than a rod attached to the PME earth, as with TT there is no risk from open PEN conductor. And for the suplimentery rod to be of any use it would need to be around the 2 ohm mark (depending on the fault) which could be hard to achieve
 
Would TT not be safer than a rod attached to the PME earth, as with TT there is no risk from open PEN conductor. And for the suplimentery rod to be of any use it would need to be around the 2 ohm mark (depending on the fault) which could be hard to achieve


I get that but it seems silly to go to the effort of isolating the extremely efficient and low resistance PME earth path and solely relying on the fluctuating and higher earth rod path.

I know this is the big debate and can see both sides. If only we had something like a regulations book to give definitive answer lol

Failing that I scrap the rod idea and just use the PME and hope that there is never a PEN Failure.

My gut is telling me that although I need to achieve the 2 ohm mark on the rod to be successful it is better being there and providing some sort of earth path than not being

Im also going to install a DP RCBO so this will disconnect both live conductors should a fault occur.
 
I never understand this instruction from a hot tub installer.... “leave an isolator and 5m of flex“

so they want you to leave a connected flex, with bare ends, and the only protection is hoping no one turns on the isolator.
even padlocking it and leaving the key in the hands of a normal person (the customer) is questionable.
 
I never understand this instruction from a hot tub installer.... “leave an isolator and 5m of flex“

so they want you to leave a connected flex, with bare ends, and the only protection is hoping no one turns on the isolator.
even padlocking it and leaving the key in the hands of a normal person (the customer) is questionable.

I know right I am planning to connect the flex up in an adaptable box and leaving the isolator switched off. That way I know the cable is terminated safely. My only concern is the hot tub company not liking it and trying to charge the customer for a return visit as they just want to see a coiled flex ready to go.

IMG_8656.JPG

This is the paperwork they provided to the customer even there so called example of the supply rough no glands on the isolator the SWA swooping and cable tied to a couple of brackets and the fact that they have left a coil of cable potentially live. this is how they are wanting the install to be left
 
These are double pole switching: Electrical Wholesaler - Hager RCBO 2P(1P+N) 6kA B-40A 30mA A Class AD940J - https://www.electricalwholesaler.ie/products/switchgearfuses/switchgeardistribution/rcboresidualcurrentbreakers/hagerrcdrccb2p40a30maaclassad940j. All the double pole switching units that are definitely double pole are two module wide, all those that say they are and are only one module wide on investigation are not.
What about the Wylex NHX miniature rcbo's, it's a switched neutral.
Wylex rcbo.jpg
 
Last edited:
I am surprised that Wylex have been able to produce a switched neutral RCBO in a single module, what surprise's me mostly is that if and I emphasise the if they are able to achieve a 3mm air gap (unverified) on both the phase and neutral in that space I would like to see how they do it, because that is what is required under EU specifications.
 
Last edited:
I am surprised that Wylex have been able to produce a switched neutral RCBO in a single module, what surprise's me mostly is that if and I emphasise the if they are able to achieve a 3mm air gap (unverified) on both the phase and neutral in that space I would like to see how they do it, because that is what is required under EU specifications.

Can't find a single module DP RCBO tear down, but here's one of the Crabtree/Wylex single module RCBO/AFDD which crams even more into the same space.

View: https://www.youtube.com/watch?v=gdVntVfP6Q8
 

Reply to Another Hot tub install in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
659
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
I have someone that wants a hot tub installing and it’ll be my first time, I have came up with anxixeaxfwanted to check it was correct. I wanted...
Replies
10
Views
1K
Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
Replies
4
Views
1K
Hi Guys So I've never installed a hot tub supply before so take it easy on me. I've spent a bit of time researching it myself and its a minefield...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock