im sure the Q 1/200+1/18+1/2.5+1/180+1/145=1/RT
I also got 2.11MOHMS
it also ask for any commets to be recorded in observations & recommendations.
so I put futher investergation of low readings of cicuits reading 18 & 2.5Mohms code 3, but circuits do comply
 
Last edited by a moderator:
Right, exam over analysed to death now not sure if I have passed, I must stop now:
Other answers:

Three conditions before MEWIC to be issued:
Do not impair safety of existing; designed constructed and tested to BS7671, complies with BS7671
(signature line on MEWIC)(only got one of these)

Prepare for IR testing:
Loads removed, sensitive devices disconnected or linked out, no shorts between conductors
(last one not precise enough, perhaps; should be L or N to E)

Insulation resistance other question resistance: as length, CSA, temperature rise:
IR Down ohm Up
IR None ohm Down
IR None ohm up

Insulation resistance calculation was just nasty getting so close to the limit
Observations: circuit with 2.5Mohm near the limit requiring investigation, may indicate circuit deterioration.

Section B
Certificates required for new installation and periodic test:
EIC with SofTR and SofI and PIR with SofTR and SofI

TNS diagram description was OK I think may have forgotten to say it was the secondary winding of the supply transformer.

RCBO test
Idn 30mA 300ms on positive and negative cycles, 5Idn 150mA 40ms on positive and negative cycles, 0.5Idn 15mA no trip on positive and negative cycles
(added +ve and –ve at the last minute)
Do Ze to ensure presence of effective earth
(I think)

Tests of lighting circuit:
Continuity, Insulation resistance, polarity, Ze,
Low resistance ohmmeter, insulation resistance tester(ohmmeter in chapter 4), low resistance ohmmeter, Earth fault loop impedance tester
(messed up the number of marks and tried to add stuff to make it up to 8 marks for each not 8 marks overall probably only got 4)
Reasons for order:
Ensure all CPC/ earth in place, ensure no short circuits/leakage, ensure no wrong connections
(really not sure about that one, can’t remember what I answered)
No instrument: Functional test at end

Sorry for the rambling on.
Hope everyone did well.
Roll on 10th October, please!
 
Last edited:
Tests of lighting circuit:
Continuity, Insulation resistance, polarity, Ze,
Low resistance ohmmeter, insulation resistance tester(ohmmeter in chapter 4), low resistance ohmmeter, Earth fault loop impedance tester
(messed up the number of marks and tried to add stuff to make it up to 8 marks for each not 8 marks overall probably only got 4)
Reasons for order:
Ensure all CPC/ earth in place, ensure no short circuits/leakage, ensure no wrong connections
(really not sure about that one, can’t remember what I answered)
No instrument: Functional test at end

Sorry for the rambling on.
Hope everyone did well.
Roll on 10th October, please!

Hi richard on the testing of the lighting circuit hope you ment Zs and not Ze.lol as all the other existing circuits that were not under test would be live with no earth. Opppps
 
Last edited:
I thought it was a very easy paper with comparison to others. Learned a good tip for remembering things to look for during periodic inspection SADCOW=SAFETY, AGE, DETERIORATION, CORROSION, OVERLOAD, WEAR AND TEAR. It might be useful in the future
 
Last edited by a moderator:
Ha Ha ha Haa YES: you have achieved the Pass standard in 2391-10!
What was i worrying about; it was dead easy, no stress, no strain, no sweat exerted.

Thank goodness for that!
and relax.
Just got to wait for the certificate now.
 

Reply to August 2391-10 taken today in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi, sorry if this is the wrong place to ask, I am wondering about becoming an electrician of some form or another and thought to come to an...
Replies
15
Views
1K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
A bit of a mini essay but these questions have been building up in my mind over the last weeks and months as I've been studying and volunteering...
Replies
6
Views
3K
Hi, I am looking to get in on being an electrician, I've been doing research and poking around here for a bit on answers and also speaking with...
Replies
9
Views
7K
I went out today to carry out an EICR on a domestic property. The lead up to the job had been confusing. The elderly (roughly @telectrix 's age)...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock