I do not insist they are the same. I insist that a TN-C-S is a TN-C but then seperated. A TN-C cannot be a TN-C-S.
Yes we know that. So OP have you worked out your cable size.
 
Yes we know that. So OP have you worked out your cable size.
Taking that the Ib is 60amps (k.m.f il install with bs1361 60amp fuse in it) distance of 80 metres will be 35mm swa having a volt drop of 6v. I believe this to be the correct size, correct me if im wrong
 
How many cores are in the cable and what %vd are you using.
 
Il give you the scenario, stables in a field, e-on have been out and put a supply in a hut with a meter on and a one shot, main fuse is 80amps, the customer need a fuseboard putting in the barn, 75metres away, what size cable would i be looking at, ive done a calculation, 1 x swa cable 3 core, burried, ive use 80amp as the demand as this is the maximum at the origin and the cable size is coming back at 25mm. Is the right or is there some sort of diversity applied which would allow you todrop to 16mm. All that will be going in are sockets and light, quite a few to be fair but altimatley just wanted to get the armoures cable to the fuseboard and just questioning the size. Any help is appreciated
 
You also need to design the sub main zs to disconnect in the required time ...
 
  • Funny
Reactions: Baddegg
Max demand in the hut will determine what fuse size to use at the origin; Volt drop at 3% will also have a significant bearing on the cable size. Knowing the type of loads, both power and lighting will also give you guidance.
You may be able to reduce several of these quantities to give you a more reasonable cable size otherwise you'll need to hire a tractor to lay the cable.....
 
I would export the PME or TN-C-S, the PEN conductor stops at the origin of the installation, so that the cable is protected by the sub-main fuse and the suppliers service fuse, and provide TT earthing rod/s or plates to give you the necessary protection at the hut/stable. That's if there are no objections ....lol
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Cable calculation
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
91

Thread Tags

Advert

Thread statistics

Created
Simon Burton,
Last reply from
ackbarthestar,
Replies
91
Views
10,634

Advert