can anyone explain why if you spur off the ring to a f/c/u the spur must be 2.5 to supply a 1.5? when would the rating exceed that of the 1.5? is if f/c/u potential change to socket the only reason?
 
Last edited by a moderator:
Because the ring will be protected by a 32a device at the CU.....not what you would want covering a 1.5mm.
The protective device at the CU should not exceed the current rating of the smallest conductor protected by it, yes I know a 2.5mm is not rated at 32a but the regs make an exception for spurs off a ring allowing a minimum 2.5 to be used.
 
Last edited by a moderator:
Hi interesting topic, if you look at the logic behind the spur from the ring to a double socket. say if you loaded each outlet outley to 13 amp total + 26A 2.5 is rated as 27Amp method C clipped direct i now the others dont work out. If you say a 13 amp spur you can only pull 13amps 1.5 is 19.5 method C so it should be ok to feed spur from a ring. I checked the regs to see if it has change but i have installed smaller cables in the past to feed a spur from a ring. if you check out regulation 433.2 see if you or any one else can throw a light onto it, from this i think you can down size providing it is protected at the other end and no longer than 3mts. :eek:
 
Because the ring will be protected by a 32a device at the CU.....not what you would want covering a 1.5mm.
The protective device at the CU should not exceed the current rating of the smallest conductor protected by it, yes I know a 2.5mm is not rated at 32a but the regs make an exception for spurs off a ring allowing a minimum 2.5 to be used.


yes clear discription and that applies to what I mean but what I'm saying is when an FCU is in the design supplying sockets for example.


so it would be: 2.5 / FCU / 1.5 - socket ( load side) as per picture in BRB.

Why not: 1.5 / FCU/ 1.5 - socket( load side) we know only one socket from an unfused spur but there is a potentialfor a DIY FCU change to socket?

If it where 2.5 / FCU / 1.5- socket (load side)/ onto FCU (from supply side) / 1.5 - socket ( load side) would that be acceptable clipped direct? or would it be better practice to extend the ring to the first FCU? I know what I would prefer to do but what is acceptable?
 
Last edited by a moderator:
Hi interesting topic, if you look at the logic behind the spur from the ring to a double socket. say if you loaded each outlet outley to 13 amp total + 26A 2.5 is rated as 27Amp method C clipped direct i now the others dont work out. If you say a 13 amp spur you can only pull 13amps 1.5 is 19.5 method C so it should be ok to feed spur from a ring. I checked the regs to see if it has change but i have installed smaller cables in the past to feed a spur from a ring. if you check out regulation 433.2 see if you or any one else can throw a light onto it, from this i think you can down size providing it is protected at the other end and no longer than 3mts. :eek:


That is pretty much the way I read it too, Providing there is no branches meaning other un-fused pull on the supply side.
 
Last edited by a moderator:

Reply to cable size in the Australia area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
668
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Im running a ring main for all my sockets using 2.5 cable....as an after thought i was thinking to spur off one of my socket outlets and run up...
Replies
4
Views
609
The customer has suggested from a previous electrician that the oven requires a new circuit installed . Upon viewing the instructions it is stated...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock