Hi interesting topic, if you look at the logic behind the spur from the ring to a double socket. say if you loaded each outlet outley to 13 amp total + 26A 2.5 is rated as 27Amp method C clipped direct i now the others dont work out. If you say a 13 amp spur you can only pull 13amps 1.5 is 19.5 method C so it should be ok to feed spur from a ring. I checked the regs to see if it has change but i have installed smaller cables in the past to feed a spur from a ring. if you check out regulation 433.2 see if you or any one else can throw a light onto it, from this i think you can down size providing it is protected at the other end and no longer than 3mts.