My next question is… how many sockets can I add? My plan is to only add the one at the moment, but may add more in future in a radial?

Would I need a switched connection unit if I was to add more sockets? The main MCB is currently rated at 16A and is also powering the garage.
 
If the supply MCB is 16A than any power cable (1.5mm or larger) is fine if not heavily insulated or hot zone and no realistic limit to number of sockets.

But...you are obviously limited to 16A total! Also some larger loads with motors like chop saws, etc, might take enough of a start-up surge to trip a 16A B-curve MCB. Going for a 16A C-curve might be an option but really then you need to do a bit more design and testing.

Ultimately your cable run and loads are limited by one or more of the following:
  • Current carrying capacity of the cable (mostly conductor size, but also thermal insulation of its route / installation method)
  • Voltage drop (should be less than 5% at max load)
  • Fault impedance to disconnect fast enough (usually met if VD met)
For guidance, a 16A circuit on 1.5mm T&E should be limited to 27m (or 15m if C-curve depending on supply Ze, typical TN-S limit). If it is in 2.5mm (more likely as safe for greater range of installation methods) then 45m (or 24m C-curve).
 
Last edited:
If the supply MCB is 16A than any power cable (1.5mm or larger) is fine if not heavily insulated or hot zone and no realistic limit to number of sockets.

But...you are obviously limited to 16A total! Also some larger loads with motors like chop saws, etc, might take enough of a start-up surge to trip a 16A B-curve MCB. Going for a 16A C-curve might be an option but really then you need to do a bit more design and testing.

Ultimately your cable run and loads are limited by one or more of the following:
  • Current carrying capacity of the cable (mostly conductor size, but also thermal insulation of its route / installation method)
  • Voltage drop (should be less than 5% at max load)
  • Fault impedance to disconnect fast enough (usually met if VD met)
For guidance, a 16A circuit on 1.5mm T&E should be limited to 27m (or 15m if C-curve depending on supply Ze, typical TN-S limit). If it is in 2.5mm (more likely as safe for greater range of installation methods) then 45m (or 24m C-curve).
Thank you. If I run in more than 1 socket, do I have to run the next socket off the previous one like a radial? Or can I run 1 socket 1 way from the junction box, and one socket the opposite way from the junction box (wago connected inside).
 
Thank you. If I run in more than 1 socket, do I have to run the next socket off the previous one like a radial? Or can I run 1 socket 1 way from the junction box, and one socket the opposite way from the junction box (wago connected inside).
You can do ether, but obviously have to have the appropriate number of terminal holes to do so (5-way Wago as they don't make 4-way).

However you do it, make sure it is obvious and/or suitably labled to allow future fault-finding. It might be someone else who knows nothing about your reasons, or you if a few years time when you forget!
 

Reply to Can I connect an outdoor socket to a junction box which feeds my garage? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I found a 13A FCU, connected to the kitchen ring supplying an outdoor junction box, providing two SWA 2.5mm radials. Unconventional? yes. One...
Replies
2
Views
813
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K
Hello, First of all, thank you in advance for any helpful insights posted in response to my question. I have just moved into a new home. With...
Replies
1
Views
1K
I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
729
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock