Based on a 240V, 7.5kw shower and a total length of 16M of 4MM2 cable and assuming cable resistance at 4.3mohm/M then my (rusty) calcs give a current flow of 30.975ohms and a shower output of 7.368kw and a voltage drop of 2.13V through the cable resulting in a cable heat loss of 65.94watts or 4.12watts/meter of cable.

So is 4MM2 suitable??.
Only if it keeps cool enough.

That is one of the 3 critical tests for cable choice:
  • Current carrying capacity (combinations of resistance, insulation temperature limit, ambient temperature, and thermal insulation "method")
  • Voltage drop (resistance and length)
  • Zs for Automatic Disconnection of Supply (resistance, length, protective device and supply impedance)
Should I don the Cardinal Ximénez outfit and summon Cardinal Fang now?
 
  • Like
  • Funny
Reactions: loz2754 and DPG
I love these convos you have to put every detail in about every product or operation. The science behind it or the physics, the calculations like you designing an electrical installation right from your phone.

If you put anything in laymans terms someone is quick to point out a fall or bite ?

Have fun guys another forum i wont be on again.

You lot are way better electricians...well done

I notice you've been back on the forum this evening. I knew you'd be back.

As I say, stick around - there's a lot of knowledge on here.
 
  • Like
Reactions: Pretty Mouth
Only if it keeps cool enough.

That is one of the 3 critical tests for cable choice:
  • Current carrying capacity (combinations of resistance, insulation temperature limit, ambient temperature, and thermal insulation "method")
  • Voltage drop (resistance and length)
  • Zs for Automatic Disconnection of Supply (resistance, length, protective device and supply impedance)
Should I don the Cardinal Ximénez outfit and summon Cardinal Fang now?
Installation method and ambient temperature takes paramount for most normal fixed wiring applications as it dictates everything else...
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Milton keynes

Thread Information

Title
Can I use a 4mm T&E for a 7.5Kw shower?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
64

Advert

Thread statistics

Created
louis butler,
Last reply from
GLENNSPARK,
Replies
64
Views
6,843

Advert