andyh

Installing first fix wiring in a new build and the kitchen will have a range cooker. There is no mains gas and bottled gas is not desirable. The cooker will therefore be all electric with an induction hob. The manufacturers website (Rangemaster) have a MAX load on the cooker of 17.4KW (around 75A). I have discussed this with their technical department and they have advised that as it's a domestic premises, you can apply diversity and therefore the working load is around 30A. They recommend putting the cooker on it's own dedicated 45A breaker with a 10mm2 cable. They have also stated these have been installed in a number of domestic premises without issue using the above recommendations.

Any thoughts on the above? :confused:
 
well diversity for a cooker is normally 10a + 30% of full load + another 5amp if there is a socket on the control unit

So it would be 10a + 30% of the FL as you say 75amp so would be 32,5amps + the 5amp if it as a socket.

Your 45amp could be a 40amp and stick with the !0mm^ but make sure that the 10mm^ will be enough if there are any de-rating factors.
 
I can't see a problem here, don't bother with the socket, but check that your consumer unit is up to the task (I think some old wylex units had a max of 60A total load) especially if you have an electric shower etc etc.
Contactor switching is often used in this situation but doesn't really comply with requirements for isolation.
 
It's a brand new Wylex CU rated at 100A. No intention of putting a socket on it. No electric showers either.

I was going to run the cooker off a contactor controlled via a grid switch. The contactor would have normally open contacts but when the grid switch was on, the cooker would be powered. Any problems with this arrangement?
 
No it doesn't. The point is I don't want an ugly cooker isolation switch and would rather control all the appliances from one grid switch. The grid switch ratings only go to 20A but utilising one of these through a contactor mounted either within the CU or next to it would allow control of the cooker via the grid switch.
 
no problem in putting cooker isolator inside kitchen unit, as long as it's accessable and within 2m of the appliance
 

Reply to Cooker Load in New Build in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hello Guys Looking for some advice with regards to a extension job. Customer has ordered a Rangemaster Induction Hob and Oven. I've looked at...
Replies
4
Views
1K
HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
Replies
18
Views
4K
Hi folks, DIYer here, hoping for some advice before most likely calling in a spark. I'm looking to wire in new cooker and hob (separate units)...
Replies
1
Views
2K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
912

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock