HI All,
I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of over 2KW should not be supplied by a ring main and should have a 4mm radial. (BS 1363)

My questions are really around this- - It seems all of my appliances exceed 2KW- So I have allocated each circuit to not exceed 30A. This gives three radial’s.

Radial 1- 2 Cookers (3KW and 3.5KW)
Radial 2 – 2 cookers (3KW and 3.5KW)
And Radial 3 - Fridge freezer 10A, 2 x dishawashers @10A each,
The Quooker (that says its only 10W?!) and drinks fridge I am suggesting to be on switched fused spurs from the ring main.

I also have washing machines and dryers going into the utility- do these also need their own dedicated radial? as once again they exceed 2KW Or have i misread the regs?
See attached all feedback welcome ;-)
 

Attachments

  • Ground Floor.pdf
    842.8 KB · Views: 12
In a brand new build I would just run in lots of 4mm radials to all the various positions. You can have a bank of 20amp circuits on Rcbos each identified what they serve at the consumer unit.
almost exactly how they do their wiring in pretty much every country in the world
 
The 2kW limit is really intended for the likes of immersion heaters that can draw that sort of power for hours at a time. Obviously for socket-outlet circuits in the UK the limit is 3kW = 13A per appliance.

Anything that takes over 3kW should be on a dedicated circuit, that could be using 4mm to 16mm cable depending on the circumstances. Quickest route is to check the on-site guide for combinations that are acceptable for your appliance load/OCPD, cable length and installation method.

As far has multiple radials versus RFC for socket/FCU-fed appliances it gets a bit religious. The comment about "almost exactly how they do their wiring in pretty much every country in the world" forgets that most of the rest of the world does not have fused plugs and so they are forced in to 20A or less OCPD and thus the diversity benefit of 32A to share over multiple variable loads, and cost savings of 2.5mm RFC in doing so, are simply not an option there.

If you want to see the debate then go here rather than starting anew:
 
Last edited:
In terms of kitchen design though a far more important detail is to have accessible means of isolation for all white goods (as well obviously for hard-wired stuff like cookers). That is now part of the Scottish building regulations but I don't know if England & Wales has anything similar.

So put 20A isolator switches above the worktop and then a 13A unswitched socket behind each fridge/dishwasher/washing machine or similar.
 
Do those regs say where the isolators have to be ?
If the CU is accessible then you have a means of isolation.
The intention is an "ordinary person" is able to switch anything off if there is a problem, or just for extra safety when doing any maintenance and without having to move a 50kg washing machine loaded with water, etc. Using the CU is fine for a sparky or competent DIY'er but not want most folks would think of under panic conditions.

I expect they would have to be accessible to a wheelchair user under building regs for any part of UK, so that limits height range and not being in cupboards, too close to corners, etc, that are unreachable from a chair.

Also you should think about what a visitor might need to do, or a future owner, not what you as the installer knows about the setup. My own preference would simply be above the appliance as then it is fairly obvious what it might do.

Some folks like the look of grid switch arrangements but others say they lack the reliability of typical stand alone isolator switches. If grid switch (also some stand-alone 20A isolator switches) you can buy switches engraved with functions like "fridge" and so to to make it clearer.
 
Last edited:
Scottish regs are here:

Section mentioning this aspect is final section:

Electrical fixtures - outlets and controls of electrical fixtures and systems should be positioned at least 350mm from any internal corner, projecting wall or similar obstruction and, unless the need for a higher location can be demonstrated, not more than 1.2m above floor level. This would include fixtures such as sockets, switches, fire alarm call points and timer controls or programmers. Within this height range:

  • light switches should be positioned at a height of between 900mm and 1.1m above floor level
  • standard switched or unswitched socket outlets and outlets for other services such as telephone or television should be positioned at least 400mm above floor level. Above an obstruction, such as a worktop, fixtures should be at least 150mm above the projecting surface
Where sockets are concealed, such as to the rear of white goods in a kitchen, separate switching should be provided in an accessible position, to allow appliances to be isolated.
 
Isolations switches goes without saying- It really is about what i can have as spurs of my ring main - and what I need radials for. This is a BC question. I don't want to run in all my cables just for some BC inspector to say "well you cant do that you muppet"
 
Isolations switches goes without saying- It really is about what i can have as spurs of my ring main - and what I need radials for. This is a BC question. I don't want to run in all my cables just for some BC inspector to say "well you cant do that you muppet"
Having an isolator switch then socket off an RFC is no different from the usual spur so you can have those at any point on the RFC. I.e. if you were putting in 4 white good points, each with an isolator switch, you would run the RFC to each switch's input (as if a socket) then have a single 13A socket off the switch output.

If you have an RFC just for the kitchen, for example, then all appliances are roughly half-way so balance is always very good. Some prefer a radial in 4mm (method permitting) to also have 32A for cases when the total load that could well exceed 20A. Swings and roundabouts really, 2.5mm is easier to wrangle at back boxes and allows a few more "installation methods", but you then have the final run back to the CU to do. Or if thinking ahead, run both legs from CU to kitchen and then close round there, etc.

The don't-do of RFC is to spur off more than a double socket. Better still, don't spur off anything without a very good reason (like isolator switch, etc) as you lose some of the advantages of better fault coverage when testing.
 
My reading of the regs says that any appliance of over 2KW should not be supplied by a ring main and should have a 4mm radial.

No, there is a recommendation for certain types of appliance over 2kW to have their own circuits, there is no requirement for those circuits to be 4mm radials.

.
Radial 1- 2 Cookers (3KW and 3.5KW)
Radial 2 – 2 cookers (3KW and 3.5KW)
And Radial 3 - Fridge freezer 10A, 2 x dishawashers @10A each,

Splitting 4 cookers across 2 circuits seems reasonably sensible.

I would put the fridge freezer on its own circuit to reduce the risk of it going off when a fault occurs in another appliance.
 
I would put the fridge freezer on its own circuit to reduce the risk of it going off when a fault occurs in another appliance.
That aspect is kind of swings and roundabouts now that RCD is pretty mandated for all domestic circuits.
  • Advantage of separate radial - fridge stays on if something else trips the RFC, etc.
  • Disadvantage of separate radial - if fridge circuit is tripped (e.g. from power surge, etc) you don't notice until you go to said fridge and find it de-thawing.
 
Just to confirm, ylu
That aspect is kind of swings and roundabouts now that RCD is pretty mandated for all domestic circuits.
  • Advantage of separate radial - fridge stays on if something else trips the RFC, etc.
  • Disadvantage of separate radial - if fridge circuit is tripped (e.g. from power surge, etc) you don't notice until you go to said fridge and find it de-thawing.

You'd tend to notice that the light in the fridge part didn't come on though.
 
You'd tend to notice that the light in the fridge part didn't come on though.
Assuming you use the fridge often enough. Probably OK in my case as cups of tea needing milk are common, but for a freezer-only that you check once or twice a week more of a concern.

I presume you get loss of power alarms for this sort of thing, but never looked/found that yet.
 
Assuming you use the fridge often enough. Probably OK in my case as cups of tea needing milk are common, but for a freezer-only that you check once or twice a week more of a concern.

I presume you get loss of power alarms for this sort of thing, but never looked/found that yet.

Yeah freezer only is a problem
 
That aspect is kind of swings and roundabouts now that RCD is pretty mandated for all domestic circuits.
  • Advantage of separate radial - fridge stays on if something else trips the RFC, etc.
  • Disadvantage of separate radial - if fridge circuit is tripped (e.g. from power surge, etc) you don't notice until you go to said fridge and find it de-thawing.

Do power surges actually trip RCDs? And wouldn't the wonderful mandatory SPD sort that out now?


Domestic fridges should hold their temperature for at least 12 hours so it should be discovered in normal use before all is lost.


Just to be pedantic I think thawing would be the problem, de-thawing would imply it is getting colder 😜
 
Do power surges actually trip RCDs? And wouldn't the wonderful mandatory SPD sort that out now?
Some models seem to be sensitive to dV/dt surges more than others. SPD ought to keep some of that down if due to a lightning spike (at least limiting 'V' so dV is a bit less).

I guess the real world risk is small, but that is the sort of thing we fixate on here as designing for fault handling is an essential aspect of safety. But flip side of that is risk of socket circuit tripping and not being noticed (or happening when on holiday, etc) is also pretty low.
Just to be pedantic I think thawing would be the problem, de-thawing would imply it is getting colder 😜
True! I had never really thought about that expression before :)
 

Reply to Kitchen Wiring-New Build ring vs radial in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
961
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
619
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
659
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock