Hi All,
My house is supplied via a PME cutout - Ze 0.07Ohm and the main CU is a 22W Split Hager Board with 2 unprotected ways and 3No banks of 4-6 circuits, each protected by a DP 80A/30mA RCCB
I've just run a supply to my shed - through the house in 6mm T&E to an external Wiska box where I've changed to 6mm 3C SWA for the onward supply to the shed.
At the Wiska box I haven't jointed the T&E CPC to either the SWA CPC or SWA Armour, which keeps the PME within the equipotential zone. The T&E CPC is terminated at the main DB so it protects the cable along it's length within the house.
The P/N of the SWA is terminated in a 2Way G/Board at the Shed which uses a 1.2m Earth Rod to complete it's TT supply. The SWA CPC & Armour are both terminated to the Garage Board MET, protecting the 'run of cable in the garden.
Ze for the Rod is 43Ohm (>21 but a lot less than 200 or even 1667Ohm)
The Incomer of the Garage Board is a 63A/30mA DP RCD and all the shed provides power to is :-
C1 - 16A MCB for Outdoor socket & Water Feature
C2 - 6A MCB for 7No 3W LED Spotlights.
The problem I've got isn't major but I'm finding when I perform an RCD test that the first device to trip is the RCD protecting the Shed Supply in the main house DB and this takes with it another 4+ circuits.
I'm not worried about nuisance tripping and realise it's just about sensitivity but wondered whether (and assuming the regs permit) I could achieve proper discrimination by fitting a Type S RCD in the main board upstream of the shed supply so in theory the Shed DB should trip first.
For clarity the main board is configureable enough that all household socket circuits could remain on non time delayed 30mA RCCBs protecting the 200/40ms tripping requirements.
Thanks in advance
Rich
My house is supplied via a PME cutout - Ze 0.07Ohm and the main CU is a 22W Split Hager Board with 2 unprotected ways and 3No banks of 4-6 circuits, each protected by a DP 80A/30mA RCCB
I've just run a supply to my shed - through the house in 6mm T&E to an external Wiska box where I've changed to 6mm 3C SWA for the onward supply to the shed.
At the Wiska box I haven't jointed the T&E CPC to either the SWA CPC or SWA Armour, which keeps the PME within the equipotential zone. The T&E CPC is terminated at the main DB so it protects the cable along it's length within the house.
The P/N of the SWA is terminated in a 2Way G/Board at the Shed which uses a 1.2m Earth Rod to complete it's TT supply. The SWA CPC & Armour are both terminated to the Garage Board MET, protecting the 'run of cable in the garden.
Ze for the Rod is 43Ohm (>21 but a lot less than 200 or even 1667Ohm)
The Incomer of the Garage Board is a 63A/30mA DP RCD and all the shed provides power to is :-
C1 - 16A MCB for Outdoor socket & Water Feature
C2 - 6A MCB for 7No 3W LED Spotlights.
The problem I've got isn't major but I'm finding when I perform an RCD test that the first device to trip is the RCD protecting the Shed Supply in the main house DB and this takes with it another 4+ circuits.
I'm not worried about nuisance tripping and realise it's just about sensitivity but wondered whether (and assuming the regs permit) I could achieve proper discrimination by fitting a Type S RCD in the main board upstream of the shed supply so in theory the Shed DB should trip first.
For clarity the main board is configureable enough that all household socket circuits could remain on non time delayed 30mA RCCBs protecting the 200/40ms tripping requirements.
Thanks in advance
Rich