The pipe stat should be on tbe return, which is at the top of the boiler.
See, I read "frost stat" and thought it should be on the incoming cold feed. The thermostat on the wall will be the frost stat, and the other will be the pipe stat.... clue is in the name, and youre right, should be on the return at the top
Exel switchfuse, apparently lights had been flickering and 3ph machines had been running with reduced power intermittently for months. We get called out as some of the electrics are not working at all and sparks are coming out of the bottom of this switch... Despite the months of warnings that something needed attention it is now an emergency and needs to be repaired immediately! :rolleyes:
It doesn't look like much but the right hand yellow contact fork has almost completely eroded away from the arcing. The blue one wasn't far behind.
Lol at least the flex looks long, perhaps it will reach the correct pipe!
Nope, only long enough to reach the flow. Better than on the gas. Boiler being moved in due course, and I can’t be arsed to replace the flex. Only been troublesome in this recent cold weather.
[automerge]1579593582[/automerge]
You should make the complaint, otherwise they may be installing them the same for any number of houses.
If the apprentice doesn't learn what they have done wrong then they will continue to do it wrong again and again, and probably teach the next person how to do it wrong.
You right of course, I had other problems with the wiring up of the CH system, which I’ve posted about.
Guess one day, he will realise his mistake; probably more embarrassed then, when he won’t have opportunity to rectify it; more learnt that way perhaps.
Thoughts on this I came across today.... ??
Those pyros aren't brilliant.....but a darn site better than the fp200's:cool:
...and get that earth clamp at the top left. What's that doing?
[automerge]1579633464[/automerge]
Similar, but a little bit worse, maybe. Sizzled for a fair while, for sure
Another nice junction in the loft above a newly installed Ensuite in an extension, wiring taken care of by the Builder's "electrician".
I like the strain relief, so when someone trips over the cables on the loft floor, the Wagos will keep the cables in place.
Cables are secured, just, not a problem then, no bare copper showing, on a combustible surface though, still seen worse.
Found this at work when asked to reinstate an extract unit.
Boss thought it may be disconnected in the DB.
Traced swa and found still conneto the trunking.
Looked on the DB and found the machine name was there but with another machine on the same circuit.
Removed the cover found this.
Machine wanted is the smaller cable.
Removed the larger cable after asking OPs about the other machine and was told it was removed a while ago.
Got the extract working and then set about tracing the other swa.
Traced to a 32A three phase socket.
The type with its own breaker.
This was cable tied to the tray work high up.
Set about removing it and found the DB end had no earth.
Thought not good but at least it was connected to the trunking properly but with no earth from the banjo to DB.
Then came the worst of it.
Remoethe top off the plastic three phase socket and found no earth at all.
The machine ran for years like this with no earth protection.
Asked the mechanical engineer and he said they had had a few dodgy sparkies in the past.