Mar 14, 2011
36
0
81
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Hello, please can anyone advise me to help decide what would be the best way to go with this earthing/bonding issue? I apologies in advance as I know there are many threads covering this, but they often deviate and do not always decisively conclude.

I have been asked to upgrade an existing Wylex BS3036 fuse board to a dual rcd unit. The fuse board is in one of 4 flats which are all supplied via a 3 phase TNS intake.

This flat is supplied via a 60A switched fused (BS3036) isolator located near to the intake. From the switched fuse is 16mm t&e to the flats fuse board.

There is currently no main bonding to gas and water.

Using the adiabatic equation, (using both tabulated and my measured values) the minimum CSA for the earthing conductor (6mm within the 16mm t&e) is adequate.
I will need to install some main bonding conductors to the gas and water as they enter the flat, and in this case I feel they could be run in 6mm CSA.

My confusion is the difference between compliance with BS7671, and adequacy defined by calculation.

Its not a problem to install 10mm main bonding as gas and water enter flat near to fuse board location, but as there is only a 6mm earthing conductor in my opinion it would not improve the safety etc of the installation.

So….. with the existing tails should I install 6mm or 10mm CSA main bonds? and might it be necessary to run in a separate 10mm or 16mm earthing conductor?

And finally if upgrading the earthing conductor is thought necessary, the obvious route (to avoid taking up carpet and floors on two levels of communal stairs) would be out, up & along the outside of the building before coming back into the flat, so the customer will need to gain permission from the freeholder.

Sorry if my post is a bit long and waffeley, but wanted to include as much info as possible to help anyone answer my question/s.

Many thanks for any replies.
 
I would do it in 10mm. The cost difference is minimal and it future proofs the bonding should the service supply increase.
 
I would run a 10mm2 earth wire with the 16mm2 twin and earth for a start, It is my understanding the earth should be the same size as the neutral conductor up to 25mm2 and then half after that, and I would run 10mm2 earths from the db to the gas and water.
 
I think 6mm bonding with a tns supply is ok as long as ze is low enough for devices to operate quick enough (ADS). But I could be wrong. My regs books in the van and I'm too ill to be bothered to check :)
 
Thanks for the replies so far.

Ok then 10mm main bonds, future proof etc no problem, done!

Ze & Zs's are all good!

So would like to get a few more views re the 6mm earthing conductor if poss.

thanks again.
 
I would run a 10mm2 earth wire with the 16mm2 twin and earth for a start, It is my understanding the earth should be the same size as the neutral conductor up to 25mm2 and then half after that, and I would run 10mm2 earths from the db to the gas and water.

Think you need to read your BS 7671 more often!!
 
  • Like
Reactions: 3 people
Thanks for the replies so far.

Ok then 10mm main bonds, future proof etc no problem, done!

Ze & Zs's are all good!

So would like to get a few more views re the 6mm earthing conductor if poss.

thanks again.

Any bonding present at the main intake MET, to the incoming water and gas pipes??
 
Each Flat is also considered a seperate intallation electrically, and requires bonding from the water and gas services at the point of entry (within 600mm etc...) in each flat, to that flats CU.

Does each flat have a local CU?
 
  • Like
Reactions: 1 person
I personally would bond the gas and water from the MET at the metering position using 10mm g&y, how many water stop taps and gas meters does the property have out of interest? Also even though it is over the top I usually run a seperate 10mm g&y from origin to sub-main along with a 16mm t+e as I prefer to air on the side of caution. In the experience of my previous installations more often than not on a TN-S system a 6mm bond is sufficient for bonding gas and water for PIR's and now EICR's but if I was installing from new it's a 10mm every time.

Hope this helps...........
 
Each Flat is also considered a seperate intallation electrically, and requires bonding from the water and gas services at the point of entry (within 600mm etc...) in each flat, to that flats CU.

Does each flat have a local CU?

More importantly does each flat derive it's supply to a local CU via a DNO meter ??...
 
I personally would bond the gas and water from the MET at the metering position using 10mm g&y, how many water stop taps and gas meters does the property have out of interest? Also even though it is over the top I usually run a seperate 10mm g&y from origin to sub-main along with a 16mm t+e as I prefer to air on the side of caution. In the experience of my previous installations more often than not on a TN-S system a 6mm bond is sufficient for bonding gas and water for PIR's and now EICR's but if I was installing from new it's a 10mm every time.

Hope this helps...........

As many flats/apartments as there is in the building, plus a main gas and water stop valve...

Not sure what your saying here, ...are you saying there is no need to bond these services to the EMT'S at each flat??
 
Service intake to MET.
And service entry into flat to each flats met.
As for the existing 6mm in the t and e.
I'd say it needs to be 10mm without checking the bgb.
 
Service intake to MET.
And service entry into flat to each flats met.
As for the existing 6mm in the t and e.
I'd say it needs to be 10mm without checking the bgb.

Obviously only if bonding is required!!
Have you tested it??
 
As many flats/apartments as there is in the building, plus a main gas and water stop valve...

Not sure what your saying here, ...are you saying there is no need to bond these services to the EMT'S at each flat??

No as I mentioned I would bond all incoming services in dwelling where I carry out work back to the MET at origin using 10mm g&y but I did a job only yesterday where there was only 1 gas meter and 1 water meter serving 3 flats both in the landlords/communal area.

I was just asking the settup at the OP's job
 
but I did a job only yesterday where there was only 1 gas meter and 1 water meter serving 3 flats both in the landlords/communal area.

I was just asking the settup at the OP's job

Makes no difference, each flat requires it's own local bonding back to it's own CU/DB, see GN8 section 5 for further details (reg 411.3.1.2), this can be done either from the entry point of the services to each flat back to the MET at the origin, or more commonly/sensibly from each flats entry point to that flats CU EMT.

As I said, each flat is classified as an individual installation as far as the regs are concerned.
 
Makes no difference, each flat requires it's own local bonding back to it's own CU/DB, see GN8 section 5 for further details (reg 411.3.1.2), this can be done either from the entry point of the services to each flat back to the MET at the origin, or more commonly/sensibly from each flats entry point to that flats CU EMT.

As I said, each flat is classified as an individual installation as far as the regs are concerned.

As I said I was asking for more info regarding the job, out of interest why would you have to bond the gas in every flat if there is only 1 meter at the property? We don't even know if there is gas in every flat. Also as I have also said I would bond every incoming service to every flat. More info that is all I was asking for fgs................
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Earthing conductor and main bonding conductor clarification wanted please.
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25

Advert

Thread statistics

Created
flyingsparc,
Last reply from
Amp David,
Replies
25
Views
4,896

Advert