Hi All

I have a customer reporting getting a shock from their electric shower, I have to go there tomorrow to investigate. Can anyone give me a heads up on what tests to carry out to prove if this is the case.

Thanks
 
Hi,
check all your main earthing and main bonding. Do a continuity of protected conductors test (should be less than 0.05 Ohms )

Do an insulation resistance test on the cable supplying the shower.
Do an R1 + R2 on the cable to the shower and a ZS test as well.

But, it does sound like an earthing problem.

Hope some of this helps, and please anyone else add some more tests that may help.

best regards to all,
Sav
 
Shower should have protection by 30mA RCD so this should be checked for correct operation as it is this that should prevent you getting shocked.
 
If there are no IR faults,earthing and bonding are in place,and adequate earth fault protection is provided they wont be getting shocks.....as the others have said this is what you need to check,
 
If there are no IR faults,earthing and bonding are in place,and adequate earth fault protection is provided they wont be getting shocks.....as the others have said this is what you need to check,


Unless there is no RCD in place and there is an internal problem with the shower.
 
Hi,
Do an insulation resistance test on the cable supplying the shower.

Sav


Is it best when doing the IR test to try with the shower switched on and do it with L&N clipped in one croc and the cpc in the other to actually check the shower as well?
 

Reply to Electric Shock from Shower in the Australia area at ElectriciansForums.net

Similar Threads

Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Hi, changed a bathroom extractor fan. Easy enough. I was dealing with a grey, black, brown and earth wire. When i tested the black wire, which i...
Replies
14
Views
1K
Hello, I have a customer who is looking to replace their electric shower. There is equipotential bonding connected to the cold feed. I’ve not seen...
Replies
11
Views
869
A pull-cord shower switch is located in Zone 2 of a bathroom, including the ceiling base containing the electrical connections. With a little...
Replies
6
Views
732
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
210

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock