Hi all

first job with enphase system all registered ok see real time data put in scoket of pv board to envoy so
on same circuit board.
put in a addon NHP2010 with HP200, NHP2010 plugged in & envoy input to this unit, HP200 at router
end plugged in, put in extra socket from consumer unit on same RCD & breaker as the router is plugged into
on domestic down stairs ring circuit, no comms over line!.
any help would be apprecaited?
work around i used 10meter patch lead & plugged envoy into router got IP address & real time data
built array issued all micro inverter serial numbers all ok just when i try wirless comms.
can you use usb on envoy?
 
We install a PV dedicated consumer unit supplied from a Henley block and then hard wire the Envoy into a dp fused spur with a 5A fuse. We then run a cat5 cable back to the router. A little extra work but good comms every time and no revisits.
 
hi Matt M
all sorted now found problem addon unit required a little set up, turn of wifi, re-set IP address,
although this was a plug & play unit & papper work was saying different.
still it works well, would like hard wired but other side of house for Cat5, i think customer would not be happy.
all units now talking to each other looks good, installed A/C isolator & small consumer unit to power for envoy unit & ran in cable to old board to ensure homeplug was on the same circuit as down stairs sockets.
MCS on wednesday, just seems to be endless papperwork trying but think i will have a few no conformities.
 

Reply to enphase envoy comms in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
A few weeks ago I posted this in another thread...: The tripping kept occurring, so I went back and moved a likely candidate circuit to the...
Replies
2
Views
1K
Hi all Recently we've been having a few issues with smoke and heat detectors.. been fitting them for years and years now mostly without any...
Replies
14
Views
2K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock