Hi Marc,
so just want to clarify, are you saying you have a smoke shaft with a AOV at the top of it then on each floor, a door opening into the shaft?
if so, I've got lots of sites on one particular contract with this set up and they have a controller on each floor in the shaft to control that door and a panel somewhere (usually top floor riser cupboard) to control the AOV. One I/O unit next to each controller and the rest is just programming which if you fit a advanced, kentec or Morley, will be easy.
Just remember it's a non blocked riser so you need a detector within 1.5m of each door.