When I use Fluke multimeter clamp-type [true RMS meter] to measure AC current in a 3.5C XLPE cable, does it give the value of leakage current or RMS value of current per phase through the cable?
 
It depends what you clamp it around.
If you clamp one conductor you will get the current in that conductor.
If you clamp all conductors (except earth) you will get the leakage current.
 
I had the weirdest issue today, brand new 1587 fc, checked a water heater on live terminal and neutral, got 600V! check neutral and earth, 0V, live to earth 230V, took the 400 clamp and got 4A. None of that made sense, the house is 3 phase, and originally the neutral and live were transposed on the waterheater, which was enough to make me start thinking i had a very large issue… so i went home and got my 907… 8.7A on both conductors, and 230 live, so theres no issue at all after all that. Any clue what on earth caused that misleading information would be greatly appreciated…
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
India
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
India
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
melvinkoshy

Thread Information

Title
Fluke multimeter current
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2
Unsolved
--

Advert

Thread statistics

Created
melvinkoshy,
Last reply from
Bruce R,
Replies
2
Views
1,087

Advert

Back
Top