Hello everyone, friends. In cases where I do not have a clamp meter, I want to measure the current drawn by the phases of a 3-phase motor with my multimeter. I left a picture below as an example. I connected my red probe to 10A., my black probe to Com. After turning the multimeter to 10A; For example, where should I connect the red and black probes to measure the current drawn by the L1 phase?

multimeter_.jpg
 
You would have to disconnect the L1 wire from the motor and put the meter in series with the connection to the motor.
You cannot do it by just probing terminals.
That is why a clamp meter is so useful, as you do not have to interfere with the wiring.

I hope you are not planning to actually do this! Much safer to use a clamp meter.

7DD2B2BD-5F06-4B11-8B63-19D801DE3B1A.jpeg
 
I hope you are not planning to actually do this!

I'm interested to know why you say this. A clamp meter is much more convenient and can be safer, but there's nothing inherently unsafe about using a meter for its intended purpose. I sometimes break into a circuit if it's likely to have a troublesome waveform that the clamp might not accurately capture, especially with DC.
 
I'm interested to know why you say this. A clamp meter is much more convenient and can be safer, but there's nothing inherently unsafe about using a meter for its intended purpose. I sometimes break into a circuit if it's likely to have a troublesome waveform that the clamp might not accurately capture, especially with DC.
To be fair, unless i knew someone's knowledge level i would not recommend this manor of testing either.

firstly they would have to figure out if the meter will survive the testing both during normal running and start up stage.

2nd it would normally require some additional conversion leads being made up to safely terminate the probes to the incoming live and outgoing motor terminal.
unlike measuring a voltage like the op was assuming where you just put the probes against something and take a reading, a good reliable connection must be maintained for the duration of the motor run, not just whilst you test it to take a reading.

and then 3rd you really need to repeat this test for the other 2 phases for the results to be a lot of use.

Edit, i am not suggesting the practice is inherently unsafe, just not something i would recommend to someone who i didn't know.

I have and am sure others have done things as a temporary rig up to test a theory that look a lot worse than that diagram above.
 
You would have to disconnect the L1 wire from the motor and put the meter in series with the connection to the motor.
You cannot do it by just probing terminals.
That is why a clamp meter is so useful, as you do not have to interfere with the wiring.

I hope you are not planning to actually do this! Much safer to use a clamp meter.

View attachment 107870
I will remove the L1 phase from the motor and connect it to the Black probe, then I will hold the red probe to the U1 input on the motor. Do I understand correctly?
 
I will remove the L1 phase from the motor and connect it to the Black probe, then I will hold the red probe to the U1 input on the motor. Do I understand correctly?
Before doing this you must first determine what the maximum start-up current for the motor should be, and that has to be less than the multimeter is rated for.

You must also be sure the meter is rated to at least CAT-III safety. This means it will have a fast internal fuse for the current range(s) and if the start-up current of the motor exceeds this by any significant amount it will blow the meter's fuse. If that happens then you will need to replace the fuse with another of the correct current and breaking capacity rating.

Making a mistake with an inadequately rated test meter can literally result in it exploding in your face. Not joking here, sadly folks have died that way.
 
The surge can be dealt with by connecting a single pole switch in the L1 supply, rather than breaking it, with the meter leads connected to each switch terminal.
Start the motor with the switch closed, and then open it.
An alternative method of measuring the run current is to fit a low value resistor in series with each supply. The resistor value and wattage should be chosen, by Ohms and Watts laws, so that there is a couple of volts or so across each resistor at the expected run current.
Measure the resistance of each resistor accurately, and then measure the voltage across each resistor with the motor running. It's then a simple matter to calculate the current in each phase.
 
Although @brianmoooore 's advice is very good and useful, I have to side with @Avo Mk8 & @James that as soon as you have to do anything fancy to safely use a multimeter, you are better to simply use a clamp ammeter.

Generally if the expected load is above an amp or so (so switch-on surge can take out 10A fuse, for example) and especially if you are trying to interrupt a live circuit or working on anything with high fault currents, then a clamp meter is the way to go.

True, the jaws can be too large for some locations, but a short length of comparable wire to give to a long enough cable to measure is about as safe & simple a change as you can make to facilitate the test.
 
I will remove the L1 phase from the motor and connect it to the Black probe, then I will hold the red probe to the U1 input on the motor. Do I understand correctly?
I wouldn't do this test by just holding the probes onto the terminal and wire, you need to figure out a way to make the probe connections more permanent and less prone to moving around or slipping.
I'd advise against doing the test this way although it's not inherently a 'bad' test there's several ways it could go pear shaped for someone that's not experienced.
 
Although @brianmoooore 's advice is very good and useful, I have to side with @Avo Mk8 & @James that as soon as you have to do anything fancy to safely use a multimeter, you are better to simply use a clamp ammeter.
Of course a clamp meter is far preferable, but my post was to illustrate that there's more than one way of killing a cat, so to speak.
Both my methods avoid the problem of switching heavy currents with meter probes.
 

Reply to Current measure with multimeter (help) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

When I use Fluke multimeter clamp-type [true RMS meter] to measure AC current in a 3.5C XLPE cable, does it give the value of leakage current or...
Replies
2
Views
871
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
9
Views
261
Hello everyone, friends. How can we understand whether the windings of the transformers we use in spot welding applications are intact? The...
Replies
0
Views
972
Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
992
I am currently looking to add 12v led cob strip lights to my mother's kitchen but confused what I need. There are currently mains wires under the...
Replies
2
Views
589

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock