Hi all,

I've just been to test a number of faults and have found a number of classrooms have relays on fluorescent lights? Can anyone think of a logical reason why someone would have installed them like this?

Thanks in advance.
 
So that they can be switched by timers and or photo cells perhaps.
How many lights to each cct, relay/contactor?
 
What he said^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^
 
Depending upon the classroom there are between 4 - 8 twin 5ft tubes per relay.

I can see any evidence of a timer, (not to ay one does not exist).
 
Currently controlled via a 1 gang switch - which is why I can't see the point of the relay.
 
its normally like that if the design current is too high for the switch, so this way the switch only carries the load of the relay
 
I haven't yet determined if all the classrooms are on the same circuit, but there is a relay in each classroom. What where you thinking?
 
the load is distributed through the relay instead of the switch. how many channels on the relays are in use?
 
Could be linked to an alarm system to switch on the lights if there is an alarm. ie the security alarm.
 
  • Like
Reactions: 1 person
you can't be looking at more than a few amps per circuit and if their controlled by a suitably rated switch can't see the point in relays really
 
Nor can I. I was trying to understand why this may a have been done as I am not familiar with use of Relays. Thanks for all the help.
 
Hi,

I've fitted them before, where this an external light sensor that switches lights off if the ambient light is good; but you can bypass this by switching the lights off/on at the switch. This was done as an energy saving measure, it's not always necessary to have lights on all the time.

Regards.
 
I worked on a few schools about 3 years ago , where we fitted Pirs through the carbon trust scheme and had to put relays in if there where 6 or more twin florrys in use , also installed relays several years ago to protect the contacts of the switch when switched of due to the back EMF ....

As already said , trace the switch feeds to the relays to where they go to..
 
Last edited by a moderator:
It could be that there's a gang of master/key switches near the entrance so the caretaker can make sure none of the lighting is accidently left on.
 
Specific lighting contactors are good for their ratings..
i.e. A 20 amp lighting contactor is rated to 20 amps for resistive, magnetic and tungsten
 
To a degree, i doubt they would be vastly different.

Cheers

They can be vastly different, the switching duty will make a big difference, one which can handle heavy inductive loads will cope with a lot more fluorescents than one only rated for resistive/light inductive loads.
 
They can be vastly different, the switching duty will make a big difference, one which can handle heavy inductive loads will cope with a lot more fluorescents than one only rated for resistive/light inductive loads.

Well the schneider 16amp contactor states 10 x 58w fluorescent, do you have an example?

cheers
 
Abb do a contactor A26 45amp (high rating than the schneider) with a 25amp CB, and that can handle 35 X 65W. I was referencing a 16 amp, do you have one in mind Dave?

Cheers
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Fluorescent lights and relays
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
31

Advert

Thread statistics

Created
Ken77,
Last reply from
Marvo,
Replies
31
Views
4,152

Advert