Hi all im looking for some advice on installing a hot tub, the supplier specifies a 16 amp type c mcb, a 20 amp rotary switch and an ip rated 13 amp socket with rcd protection, the run of swa cable from the consumer unit to the rotary switch is 30m, I will then run an swa from the rotary switch to the ip rated 13amp socket for the hot tub to be plugged in direct, what im needing advice on is the voltage drop, the cable will be clipped direct to a wall, 30m run, ive worked it out that there will be a voltage drop of 10.5v which works out at a vd of 4.6%, do yiu agree that a 2.5mm swa cable will be more tham man enough to run the hot tub, cheers.
 
it works out 2.208 on your calculations ,but 2.5 swa would go ,but how ever 4.00mm /20amp i would use .but I'm not doing the job .considering you are designing it its your call the end of the day , what is the loading of the hot tub kw .
 
  • Like
Reactions: Mikey10695
it works out 2.208 on your calculations ,but 2.5 swa would go ,but how ever 4.00mm /20amp i would use .but I'm not doing the job .considering you are designing it its your call the end of the day , what is the loading of the hot tub kw .
Hi the hot tub only draws 13amps as its a plug and play,
it works out 2.208 on your calculations ,but 2.5 swa would go ,but how ever 4.00mm /20amp i would use .but I'm not doing the job .considering you are designing it its your call the end of the day , what is the loading of the hot tub kw .
Hi the hot tub only draws 13amps its a plug and play cheers
[automerge]1593455281[/automerge]
it works out 2.208 on your calculations ,but 2.5 swa would go ,but how ever 4.00mm /20amp i would use .but I'm not doing the job .considering you are designing it its your call the end of the day , what is the loading of the hot tub kw .
Hi Ive worked out the voltage drop to be 7.41 volts, mV/a/m x Amp x Metre /1000 = 19 x 13a x 30meters /1000 = 7.41 vd
 
Last edited by a moderator:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
hot tub installation
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
Mikey10695,
Last reply from
Mikey10695,
Replies
2
Views
1,324

Advert