nickblake
Ive taken over a job from another spark who never turned up ,embarrasing because i know and have alot of respect for the guy .first thing i noticed was the supply cable 6mm 2 core swa from the house to a meter box, (looking at the load i felt this should have been at least a 10mm) then from there to a caravan which is on a 16 amp socket and the Pen conductor is to an earth rod , then in a 6mm 3 core SWA to the hot tub ,the Ib is 27.9 amps and the cable length from the house to the hot tub is 30 m with a 63 rotary switch to isolate calculating the voltage drop is 6.11 v so thats fine ,Zs is 0.91 a little hig but still within when all is running the supply voltage drops around 8 volts the installation is protected by 2 RCD's one RCBO 40 amp in the house and a main switch RCD in the meter box hot tub then protected by a 32 amp mcb,i knoe the RCD 's should be time delayed but are not and the current rating is a little to high for theincomming cable but that will be delt with the main problem is for no apparent reason the hot tub cuts out at random times ,the hot tub guy says its the supply as it drops when the heaters and pumps are on ,but i dont thing so , i feel its the hot tub ,what do you guys think any idea's