I have been inspecting and testing for some years and have until now believed that I have been doing it correctly. I spent some time at a property yesterday for a landlord doing a condition report for a rental property.
there were many many issues with several clearly being in my opinion C2. one point really confused me, (well not until today),
There was a standard electric hob at 6Kw , and a separate double oven at 4.4kw. Both were wired into their own 13amp SFU. the oven actually had 0.75mm flex going to a piece of 6mm T+E which then went to the 13amp fuse.
The oven sfu actually went back to a 6mm t+e 32amp supply to the consumer unit.
The hob was connected to the ring main.
I check the manufacturers instructions and they both stated a 32amp supply hard wired was needed.
I advised the Landlady who said the oven had been installed by e reputable supplier and had the safety certificate to prove it. She had also spoken to another engineer who had said that I was wrong to pick it up as the safety was the 13amp fuse, which would have blown.
I have issues with this, well all of it actually, but honestly, where does this situation stand with the condition report. In my opinion it is at least a C3 but possibly a C2.
I am not looking to get slagged off but just seeking some direction.
kindest regards
there were many many issues with several clearly being in my opinion C2. one point really confused me, (well not until today),
There was a standard electric hob at 6Kw , and a separate double oven at 4.4kw. Both were wired into their own 13amp SFU. the oven actually had 0.75mm flex going to a piece of 6mm T+E which then went to the 13amp fuse.
The oven sfu actually went back to a 6mm t+e 32amp supply to the consumer unit.
The hob was connected to the ring main.
I check the manufacturers instructions and they both stated a 32amp supply hard wired was needed.
I advised the Landlady who said the oven had been installed by e reputable supplier and had the safety certificate to prove it. She had also spoken to another engineer who had said that I was wrong to pick it up as the safety was the 13amp fuse, which would have blown.
I have issues with this, well all of it actually, but honestly, where does this situation stand with the condition report. In my opinion it is at least a C3 but possibly a C2.
I am not looking to get slagged off but just seeking some direction.
kindest regards