Discuss insulation res testing? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
brs73
what methods do people use for testing insulation resistance on lighting circuits,when there are loads of transformers on the circuit?
Agreed, I always put down that Ins Res..' between L & N on lighting circuits as a limitation.
Even though you know that the readings will be OK, you'll alway get some Smart Alec saying 'did you disconnect all the fittings / remove all the lamps??'
Hey.
It depends what voltage you are testing at. Really you should be disconnecting all the transformers and other electronic equipment and testing at 500V - the minumum acceptable being 1Mohm but really should be greater than 200Mohm.
If you have to test at 250V, even though the minimum acceptable is 0.5Mohm, this would only be for a SELV circuit so really the minimum for this would be 1Mohm also but as I said really should be greater than 200Mohm.
Cheers
Reply to insulation res testing? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all, if I’m getting an insulation reading of 0.03 across N & L on a lighting circuit what would cause this? Neutral earth, live earth, are in...
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Quick question. I am new to electrical installation so please be patient. You guys are great at answers. Re Insulation Testing. Why if I test...
Hi All DALI lighting system distributes circuit via LCM's, for electrical test, do you stop at the LCM or light point. how do you carry out...
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...