Hi guys, i attended a property on friday the tenant has stated the rcd is tripping at intervals of 45-60 mins, i separated the ring legs and upon testing i was getting a reading of 0.60Mohms between Line-cpc on one end of the cable with all loads disconnected, i have never come across this fault before and my question relates to the tripping characteristics of the rcd/mcb. is this a problem you guys have come across before and should the mcb be tripping out although i know the rcd is more sensitive? many thanks in advance.
 
So..........what was tripping?

Mcb or Rcd?

Or Rcbo?

Give us a clue mate :)

Rcd .......earth fault.

Mcb .............short cct/overload/earth fault.
 
600,000 Ohms. Thats alot of Ohms!

did you test the RCD as well. Just to be sure. Seems a bit high for an RCD to trip but who knows whats going on there.
 
  • Like
Reactions: 1 person
Thanks for the feedback rcd was operating fine following a ramp test and testing at half 1x and 5x
 
Hi guys, i attended a property on friday the tenant has stated the rcd is tripping at intervals of 45-60 mins,

think.........

45-60 min intervals................mmmmmm

Timeclock/pump with level switch/heating pump..............possibilities are endless but easy really when you think about it:)

Well...........sometimes lol
 
lol but are you saying the the <1Mohm reading between line to cpc has nothing to do with it? even when i attended i forgot to mention(my bad) the rcd got to a point where it was constantly tripping even with all loads plus boiler disconnected sorry if i sound like a complete novice
 
mmmm

If you have an RCD tripping with everything disconnected on the outgoing terminals then..............well..........c'mon?
 
Shane, snapped a picture of you going to work chap...

2200991.jpg
 
  • Like
Reactions: 5 people
All jokes aside i understand the fact of mcbs tripping at under <1Mohm my original question was in regards to how the mcb could/should react with the rcd in line with this type of fault, although you may already have had your kicks for the night
 
"i have never come across this fault before and my question relates to the tripping characteristics of the rcd/mcb. is this a problem you guys have come across before and should the mcb be tripping out although i know the rcd is more sensitive? many thanks in advance."
 
All jokes aside i understand the fact of mcbs tripping at under <1Mohm my original question was in regards to how the mcb could/should react with the rcd in line with this type of fault, although you may already have had your kicks for the night

Shane..............there are many on here willing to help but your post doesn't make sense mate.
You said Rcd was tripping.............that's an earth fault..........think about it!
 
  • Like
Reactions: 1 person
Shane. The RCD is either detecting a earth fault or its faulty. As for you IR on the CPC to Line being 0.6 Meg that should not trip the RCD . 230/0.03=7666 Ohms which is a long way off 600000 Ohms . Are you sure that nothing else is connected and if so I would IMO exchange the RCD and locate the IR fault that you have !
 
Thanks for the feedback Tony, I am visiting again tomorrow to try and reinstate the other half of the circuit, I will make sure I check for anything that I may have missed and recheck the rcds operation, many thanks.
 
  • Like
Reactions: 1 person
Thanks for the feedback Tony, I am visiting again tomorrow to try and reinstate the other half of the circuit, I will make sure I check for anything that I may have missed and recheck the rcds operation, many thanks.


Shane1089


would be good to hear what you find & what it was in the end :-)
 
Well it's not in the best of taste imo. Outspoken - I hope you have the guy's permission to post that photo?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Intermittent Rcd Tripping
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
Shane1089,
Last reply from
kerr82,
Replies
24
Views
4,582

Advert