Discuss Intermittent Rcd Tripping in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
S
Shane1089
Hi guys, i attended a property on friday the tenant has stated the rcd is tripping at intervals of 45-60 mins, i separated the ring legs and upon testing i was getting a reading of 0.60Mohms between Line-cpc on one end of the cable with all loads disconnected, i have never come across this fault before and my question relates to the tripping characteristics of the rcd/mcb. is this a problem you guys have come across before and should the mcb be tripping out although i know the rcd is more sensitive? many thanks in advance.
So..........what was tripping?
Mcb or Rcd?
Or Rcbo?
Give us a clue mate :)
Rcd .......earth fault.
Mcb .............short cct/overload/earth fault.
600,000 Ohms. Thats alot of Ohms!
did you test the RCD as well. Just to be sure. Seems a bit high for an RCD to trip but who knows whats going on there.
think.........
45-60 min intervals................mmmmmm
Timeclock/pump with level switch/heating pump..............possibilities are endless but easy really when you think about it:)
Well...........sometimes lol
lol but are you saying the the <1Mohm reading between line to cpc has nothing to do with it? even when i attended i forgot to mention(my bad) the rcd got to a point where it was constantly tripping even with all loads plus boiler disconnected sorry if i sound like a complete novice
mmmm
If you have an RCD tripping with everything disconnected on the outgoing terminals then..............well..........c'mon?
Shane, snapped a picture of you going to work chap...
All jokes aside i understand the fact of mcbs tripping at under <1Mohm my original question was in regards to how the mcb could/should react with the rcd in line with this type of fault, although you may already have had your kicks for the night
Reply to Intermittent Rcd Tripping in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Hi All, Weird matter happening here and I hope you can help! My 3 Pahse EC Fan is connected to a sensor and a controller for the temperature...