it proves tha there is no breakdown of insulation between live conductors and earth, so when you throw in a RCD it won't trip.
 
the clue's in the name - insulation resistance. you're testing to prove the integrity of the insulation.

testing between live+neutral and earth is normally carried out when there are loads on the circuit that you can't remove.
 
All switches closed, switch two way switching, if you can remove lamps then good, but should not be required. Surge protection devices on socket extensions cause problems though.
 
is the test still with all switchs closed and bulbs out?

tests should be carried out by operating the switches one at a time, with additional tests for every flick of the switch. remember, you want to ensure that none of the circuit insulation is defective - not just the insulation up to the switch.
 
cheers guys , i was meaning more on EICR if the light have been working perfectly fine with no faults , no tripping , then what does the L&N to E prove , tel cleared it up with insulation breakdown
 

Reply to IR test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
640
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
675
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
698
Just wondering if someone could help provide an explanation as to why this might be the case when testing an RCBO. Testing the RCBO at the DB...
Replies
7
Views
288
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
418

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock