Hi all,

Testing question for you.

I'm currently testing an existing domestic installation. The wiring is about 20-25 years old.
We have rewired some of the older circuits and added newer circuits too. During my insulation resistance test, over two-thirds of my results were coming out at 500MOhms. These circuits had new cabling and older cabling on them.
I know its unusual to get such high (perfect readings) like that, so my question is, would the fact that I'm testing through older cables with newer cables bring the IR reading up? The only other circuits that are lower than the 500 are circuits with only the older cabling on them. I have switches on for lighting circuits, no loads connected that would alter results

Any advice would be greatly appreciated.
 
Resistances will normally be lower than the lowest section of cable being tested.
Some older cabling does still measure out perfectly so by reducing the amount of older wiring you are increasing the probability of getting perfect readings.

I would expect new wiring to measure off the scale unless damp from plaster etc was an issue.
 
Is this L to N readings?
Disconnected loads, but what about electronic dimmer switches, usb charger sockets, smoke detectors?

Might be worth splitting circuits down and locating what stretch of cable is low
 
Resistances will normally be lower than the lowest section of cable being tested.
Some older cabling does still measure out perfectly so by reducing the amount of older wiring you are increasing the probability of getting perfect readings.

I would expect new wiring to measure off the scale unless damp from plaster etc was an issue.
Thanks for the reply Ferg. I pretty confident I'm testing correctly, but just wanted a 2nd opinion. Thanks
 
It's not uncommon to get perfect results on an old installation. Cables lasts a lot longer than people think. I've tested housing estates that haven't been touched for 50 years and the majority had perfect results and the ones that didn't had the dreaded cable cancer.
 
I generally try the clips together to make sure I get zero before proceeding.

On some testers it’s easier to make daft mistakes than others. E.g Metrel uses the brown and blue leads for IR and the brown and green leads for continuity. I occasionally forget to swap over! Megger is much easier as the same two do nearly everything.
 
My tester goes up to 2000M ohms and even on brand new wiring it rarely hits that target, sometimes it will show something random like 1746 or 1838, I think it just picks any old number and displays it. Even some new circuits measure fairly low though, I had 150 or so on a brand new lighting circuit recently but it had just been plastered and there was condensation everywhere.

I also think some LED batton fittings or the discos are leaking a fair bit to earth under test to reduce the values a fair bit - yes I know you are supposed to disconnect everything like this to test properly but if L-E are ok and N-E are ok then L-N must be ok seen as it has the earth in between the two of them and if you've wired it wrong you will soon know when you energise it all.

Saying nall that though, does it really matter what the reading is in the grand sceme of things 150M ohms is still 150 million ohms resistance, you won't get much current flowing through that.

Google says

Current (I) = 1.5333333333333E-6 ampere (A)

Power (P) = 0.00035266666666667 watt (W)
 

Reply to IR testing in domestic dwelling in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
630
Hi. The question is..... can saturated ground affect earth resistivity testing equipment? Some days there's an unacceptable earth reading, another...
Replies
8
Views
352
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
625
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
272

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock