Discuss Large oven tripping RCD in the UK Electrical Forum area at ElectriciansForums.net

think he means if the PF is below unity, e.g.0.8 or less. i'd like to know why it might cause rCD tripping though. in this situation, I'd shift the oven onto a 40A RCBO and see if it held.this would eliminate cumulative leakage.
Yeah me as well but I was being or trying to be diplomatic.
 
Yes figures on the IR test. And test the appliance too. In fact, do that first. After you have corrected the MCB size on that circuit.

Oh hold on. If you are a trained electrician, you really need to check your college notes. You have forgotten some essential basic things.
College notes?
 
Technically speaking 6mm cable of a 50a mcb is a no no , it either needs to be 10mm or reduce the mcb to a 40

But I have seen an experiment done by J.W where he gets some 1.5mm clipped direct cable to draw very near 70 amps for a considerable length of time before starting to smoke.



Back to the OP , my single build in oven has the strange tendency to trip my house rcd from Time to time
 
Last edited:
As an RCD is a current operated device, why would the 'power factor' have anything to do with it tripping? The power factor is related to the cosine of the angle between the voltage and the current.
An RCD operates on earth leakage, Jim, it is not an OCPD!
 

Reply to Large oven tripping RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I've recently had an oven installed by AO and afterwards I noticed in the installation instructions that the electrical connection needed...
Replies
1
Views
1K
Hello Guys Looking for some advice with regards to a extension job. Customer has ordered a Rangemaster Induction Hob and Oven. I've looked at...
Replies
4
Views
1K
I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault: I have a new kitchen fitted and two...
Replies
10
Views
2K
My Neff oven is approx 10 years old and has worked normally,until about a few months ago when it has started to trip on RCD when at high...
Replies
2
Views
1K
Hi all, Curious one and hopefully some one of you could give me some advice. A customer has had a steeltech shed installed at their premises. A...
Replies
17
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock