I've just been asked to install a lighting circuit in singles in round plastic conduit but also have a grid switch with an emergency key switch to an emergency light. Trouble is and I know some of you may be thinking how is he even qualified but I've never used singles. Ive been a house basher all my time Is it possible someone could give me a step by step?? Do you take the feed to the em light then to other lights and have seperate switches? Be nice please guys
 
Have you tried searching for forum for info?
It's frowned upon to give 'step by step' advice on here.
Do a search and come back and tell us how you think you should do it. This will give you knowledge and we can correct anything then or suggest better ways.
 
What Spoon said
 
I've just been asked to install a lighting circuit in singles in round plastic conduit but also have a grid switch with an emergency key switch to an emergency light. Trouble is and I know some of you may be thinking how is he even qualified but I've never used singles. Ive been a house basher all my time Is it possible someone could give me a step by step?? Do you take the feed to the em light then to other lights and have seperate switches? Be nice please guys
the advantage of using singles is that you can take L to switch and S/L to fittings, taking the N direct to the fittings. now work out what does what and come up with a sketch. we can then advise if it's OK or needs improvement.
 
  • Like
Reactions: I2C
From my experience it’s also got me in the client’s good books by wiring into the switch first and then into the key switch, so when the annual inspection/flick tests are done only the emergency lights are only affected. Otherwise the inspections will need to be done out of hours.
Also if they are unspecified as maintained or non maintained, I think it’s best to future proof and wire as maintained at all emergency points just incase. Little expense at this stage! As for wiring the circuit, it’s simple stuff.
 
  • Agree
Reactions: 1 person
Ask the person who did the emergency lighting design to confirm how they intended for it to be wired.
 
From my experience it’s also got me in the client’s good books by wiring into the switch first and then into the key switch, so when the annual inspection/flick tests are done only the emergency lights are only affected. Otherwise the inspections will need to be done out of hours.

The wiring should be carried out in accordance with current standards not just what gets you in the clients good books.
Testing will probably need to be done out of hours regardless as you need to allow enough time for the batteries to fully charge before the building is occupied again. That is unless other arrangements are made to provide emergency lighting whilst the batteries are re-charging.
 
  • Informative
Reactions: I2C
the advantage of using singles is that you can take L to switch and S/L to fittings, taking the N direct to the fittings.
Completely agree. When using singles, the permanent-line usually goes directly to the switch rather than the light.
In all honesty it doesn't strictly matter, the advantage of using singles is that your circuits can be shorter, by connecting from A-B directly instead of requiring additional planning to efficiently use cable.

Testing will probably need to be done out of hours regardless as you need to allow enough time for the batteries to fully charge before the building is occupied again. That is unless other arrangements are made to provide emergency lighting whilst the batteries are re-charging.
A very good point! While occupants are present, the emergency lighting must have enough charge to allow operation for a set amount of time, should such a scenario take place.

My only other advice regarding singles is to ensure line and neutral run through the same orifice of a metallic enclosure to avoid eddy-currents.
 
Completely agree. When using singles, the permanent-line usually goes directly to the switch rather than the light.
In all honesty it doesn't strictly matter, the advantage of using singles is that your circuits can be shorter, by connecting from A-B directly instead of requiring additional planning to efficiently use cable.


A very good point! While occupants are present, the emergency lighting must have enough charge to allow operation for a set amount of time, should such a scenario take place.

My only other advice regarding singles is to ensure line and neutral run through the same orifice of a metallic enclosure to avoid eddy-currents.
They would have to if the lights were wired in conduit, you wouldn't normally use singles any other way, I did say NORMALLY
 
You been on holiday @I2C ?
11 days...wow... I forget stuff after 30 mins....
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Lighting with key switch
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
12

Thread Tags

Advert

Thread statistics

Created
Craig Boyd,
Last reply from
I2C,
Replies
12
Views
2,054

Advert