Discuss low insulation resistance on 35mm lsoh cable in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

M

markmca_no1

Looking for some advice.currently doing a install of a block of flats fed from a bemco using 35mm aluminium split concentric cable low smoke.tested the cables and getin low readings of around 40 mega ohms on all between neutral and earth.1 cable is only 3 metres long.any one ideas why there
so low
 
maybe a bit of damp. leave the IR tester connected for a minute, see if the reading increases.
 
Has the end of the cable been left in water for a length of time like a puddle in storage? ... its possible if your meter is to be believed and the batteries aren't low and its calibrated regular that its drawn the water in through capillary action, the extent of this depends on the make up of the cable.
 

Reply to low insulation resistance on 35mm lsoh cable in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
During an insulation resistance test IR at an EICR I measured 0.0014 MegOhms from line to earth. When I disconnected the neutral from the neutral...
Replies
4
Views
1K
Was testing a 3 phase DB for storage heating. While testing I noticed I was getting continuity between 2 of the circuits, which were on separate...
Replies
13
Views
2K
Been to a fault finding job and lights where tripping the rcbo. After further investigation we found that it was a blue strapper cable (old...
Replies
17
Views
3K
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock