Hi. I don't know if anyone can help or shed any light on this one.
I installed a new circuit in my sons garage. 2.5 T&E clipped direct, 4x metal clad sockets and back boxes.
I haven't terminated it into the CU yet as I need to get a RCBO.
I just got everything in place and did dead tests.

End to end L 0.21Ohm
N 0.21Ohm
E 0.02 Ohm

IR >1000 Mohm

There is nothing connected in the board so no parallel paths.
I had my yearly assesment today and I asked the assessor and he couldn't think of why it would be so low.
Any one any ideas?
Thanks
 
Hi. I don't know if anyone can help or shed any light on this one.
I installed a new circuit in my sons garage. 2.5 T&E clipped direct, 4x metal clad sockets and back boxes.
I haven't terminated it into the CU yet as I need to get a RCBO.
I just got everything in place and did dead tests.

End to end L 0.21Ohm
N 0.21Ohm
E 0.02 Ohm

IR >1000 Mohm

There is nothing connected in the board so no parallel paths.
I had my yearly assesment today and I asked the assessor and he couldn't think of why it would be so low.
Any one any ideas?
Thanks


Poor connection on your MFT?
 
Nope. Checked it half a dozen times. same result. Checked it with my other mft, same result.
 
Excuse me for silly suggestion (just a trainee) but no parallel paths like cable armouring (I know you said T+E, just trying to have a go at helping) :willy_nilly:
 
They haven't put in a 10mm CPC in the T+E have they?

Honestly this defies logic. You obviously have a ring on your r1 rn and so by rights your smaller CPC should be higher on r2.

All I can think of it start to break the ring down, it's only 4 sockets and test the cable from CU to Socket 1 and then Socket 1 to 2 and go round the ring
 
  • Like
Reactions: 1 person
Thanks for the replies.
(Hightower) No parallel paths. End to end on drum, I will try that. It was a new 100Mt roll.
(Steve) It's a double garage, the CU is in the garage. so total ring about 15/20mts? They are fixed to a breeze block wall.
(malcolm) Will do, I will be going back there next week to finish off, so I will try that.
 
Thanks for the replies.
(Hightower) No parallel paths. End to end on drum, I will try that. It was a new 100Mt roll.
(Steve) It's a double garage, the CU is in the garage. so total ring about 15/20mts? They are fixed to a breeze block wall.
(malcolm) Will do, I will be going back there next week to finish off, so I will try that.
Metal sockets? if so remove the front plates from the back box and dis the fly lead (if you have one) and re test r2
 
Right just checked the rest of the roll.

L 0.37
N 0.37
E 0.67

Which is what you'd expect. So why it is down on the install I'm stummped.
 
Pete, yeah will try that also.
 
Right just checked the rest of the roll.

L 0.37
N 0.37
E 0.67

Which is what you'd expect. So why it is down on the install I'm stummped.


Have you responded to post 10 yet?
 
Sorry wrote it out then got sidetracked.

Pete, yeah will try that also.
 
Sorry wrote it out then got sidetracked.

Pete, yeah will try that also.

Please do I'm clutching at straws but I may be onto something
 
  • Like
Reactions: 1 person
It looks like I might be up there on Saturday so will try things out then.
I will post back
Thanks
 
I reckon the wall is damp and the low reading is via the 'fabric of the building' with metalclad sockets being used.
 
  • Like
Reactions: 2 people
I reckon the wall is damp and the low reading is via the 'fabric of the building' with metalclad sockets being used.

See post 10 I asked the OP to remove socket fronts and fly leads and retest he is going back Saturday to do just that.
 
  • Like
Reactions: 2 people
Damp walls is my guess too. Had this before.
 
Hi all.
Didn't have time to do any electrical work on Saturday. Was helping him move all his stuff from the old house.

Dave & Matt. Yes I wondered if it could be the building that was bringing it down, but I had never come across it before.
 
  • Like
Reactions: 1 person
I agree with Pete and Dave - the sockets and backboxes will all be earthed, but also there will be some kind of parallel path via the mass of the building, like with a TT system. The building won't even need to be particularly damp for this either. As Pete says you could disconnect all the flyleads and leave the socket fronts hanging in mid air and test to prove this, but a low R2 is a good thing.
 
  • Like
Reactions: 1 person
Damp? What's it damp with, mercury? A dripping wet wall might get you 0.02 MΩ but not 0.02Ω. Taken at face value (which is not always right with 1 s.f. on low resistance tests) 0.02Ω is equivalent to about 1.5m of 1.5mm², so the socket boxes are probably connected directly together with a large chunk of metal. Perhaps the fixing screws have gone through metal studwork or a plaster bead or similar.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Lincoln
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Low R2
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25

Thread Tags

Advert

Thread statistics

Created
Malcolm,
Last reply from
Lucien Nunes,
Replies
25
Views
2,252

Advert