Hi,

Recently i carried out a periodic inspection report. It was on a house that had a separate boiler house. The boiler house had a light, a few spurs for the boiler and heating pump. It was an oil fired boiler and i placed a defect on the report as the incoming metal oil supply pipe had no main protective bonding conductor to it. Am I right to defect this? One of my bosses said it wasnt necessary to defect it as "it was a separate building" however i still disagree. What do you think ? :confused:
 
seperate building = seperate supply = seperate test

if the oil supply pipe goes into the house it should have a bonding conductor run from within 600mm of entering the house and running directly back to the CU or MET

from the point of entry into the house is your concern, this is the equipotential zone in theory. but in your circumstance i would say that if the sockets are supplied from the house therefore they are a part of your inspection ande the CPC extends the equipotential zone and the tank should be bonded as it has the potential to become live under fault conditions.

the code 4 is a personal decision, you being the competent person are the duty holder throught the test/inspection

is there an earth spike on the tank or any of the supporting framework? if not i honestly think you'd be justified to add it as a code 1, bonding conductors are a neccessity, end of!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Main protective bonding conductor help
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
Adz,
Last reply from
uksel,
Replies
1
Views
4,912

Advert