Hi - May need some more info to be helpful.
But if you started with Ze of 0.3 on TNS and added some decent sized cable for submains and are now getting over 3 Ohms earth loop impedance, then I'm guessing you've either got a poor connection or a very very long sub mains.
If you have a 400A 60947-2 device then the cable is somewhat large. You have a Zs of 3.15 ohm, now unless this is of considerable length you must see something is not correct.
Reply to Max Zdb TNS system help in the UK Electrical Forum area at ElectriciansForums.net
Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...