Had a bit of a brain freeze. Got to go and do an inspection on a property with 2 consumer units, the 2nd fed from the first on a 50A MCB.

Let's say theoretically I get 0.2 for the Ze on the main board, then 0.3 for the Zdb at the second board and 0.2 for R1+R2 on a ring final on a 32A MCB.

Is my max Zs for this circuit 0.7 ? Max Zs = Ze + Zdb + (R1+R2)
 
The measured Zdb for the 2nd board incorporates the earth path of everything up to that point.
So the Max ZS for the ring final circuit on the 2nd board is the dead R1+R2 result added to the Zs at 2nd DB.

So in your example it would be 0.3 + 0.2 = 0.5
 
Last edited:
  • Like
Reactions: Dartlec
To add, that will include parallel paths if bonding is connected at 1st DB, so if you are wanting to calculate Zs for a circuit on the 2nd DB it would be more accurate to add:
Ze + [(R1+R2) of distribution circuit to 2nd db] + [(R1+R2) of final circuit]
 
Great, thanks for the explanation, I did wonder if I needed to treat the connection between the boards as essentially it's own radial circuit
 
Is my max Zs for this circuit
The 'Max' Zs permitted will be determined by the OCD used for that final circuit.
The 'actual' Zs will be the sum of parts upto then eg Ze + R1+R2 dist'n cct etc etc.
 
  • Like
Reactions: timhoward

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Max Zs multiple boards
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
4

Thread Tags

Advert

Thread statistics

Created
vwes59,
Last reply from
DefyG,
Replies
4
Views
3,105

Advert