Discuss Max Zs values for BS88 types gM in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

I believe the gM type operate at 7 times the In rating for a 5 second disconnection.

So a 63A for example would have a max Zs of 230/(7X63) = 0.52 Ohms
 

Reply to Max Zs values for BS88 types gM in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi All, Can anyone help with calculating a Zs value for the fuse described in the title. The fuse sizes in Fig 3A3(c) of the 18th edition wiring...
Replies
1
Views
983
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
1K
Given the RCD pictured below With the manufacturers instructions here: Am i right in interpreting that as well as being able to bring the...
Replies
4
Views
382
Any ideas on the Max Zs on a 3871 Type 3 13 amp MCB
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock