Technically yes - but if you see that sort of impedance you have a whole lot of other questions to be asked as very, VERY likely there is something seriously wrong.

If you have a TN earthing system then your CPC is unlikely to be less than 37% of the phase conductors' size (thinking 4.0/1.5 T&E here as worst-case) so if it were genuine no-fault Zs of 1.6k that implies about 1k for the line and your 5% drop is going to be a load of 11mA so basically a 2.5W bulb maximum (ignoring lamps should be 3% drop for now). Is that realistic?

Also your cable, even if 1mm as smallest / highest resistance in use for fixed wiring, would be over 36km long. Again is that realistic?

The answers are no. So in the TN case anything beyond an ohm or so points to a fault, and for that passing the RCD's limit is not acceptable - it has to be fixed.

For TT earthing again it is simply pointing to a fault. The regs say no more than 200 ohms Ra (Table 41.5 Note 2) for a reason - anything more points to a faulty rod (probably corroded badly or broken connection and bearly the wrie in contact with Earth) or one in very dry / rocky ground which is not fit for purpose - it needs to be deeper to find moisture, etc.
 
In any case it wont be for fault protection unless its TT earthing.
over 200 ohms Ra is considered unstable .
Your better off conducting R1+R2 and comparing these to the maximum ZS (roughly) , this will also ensure that it disconnects during a line-neutral short circuit.
 
Short answer: yes the max Zs for a circuit protected by 30mA RCD is 1667 ohms, and this value is what you would write on the cert. As above though, an actual measured value approaching even a fraction of this indicates other issues.

Also: You can use RCDs for fault protection on TN-S and TN-C-S installations. The regs say so, and there is a list of standard circuits in chapter 7 of the OSG that rely on RCDs for earth fault protection. There's nothing I'm aware of that suggests that overcurrent protective devices are preferred for earth fault protection in TN systems.
 

Reply to Maximum Zs on circuit protected by RCD - 1667? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
352
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
207
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
481
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
746

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock