Yes, me again, heres the scenario, customer calls in and they say the property is empty and there has been some units recorded on the meter, we install a check meter and shows the meter to be accurate. I have heard of electrical leakage, not sure if thats the right way to describe it.
The question is how do I explain this to them in an easy way ? And how would an electrician test for this leakage.
Leakage in the conventional sense comes from two main sources; resistive leakage due to insulation resistance that is less than infinite, and capacitive leakage from cable capacitance and suppressors in equipment that is connected but switched off. Neither is likely to register on a meter, unless something is seriously amiss.
Capacitive leakage has near zero power factor, so although it can clock up a few milliamps in a large domestic installation resulting in one or two VA being consumed, the real power is more likely to be in the order of a few tens of milliwatts.
Resistive leakage on a system with barely acceptable insulation, say 1MΩ from L-E and L-N, will pass 2x230/1M = 0.5mA, for a power consumption of 230x0.0005 = 100mW. It would take 10,000 hours (417 days) to consume one unit (kWh).
Therefore it is likely to be actual equipment that is consuming the power, such as the aerial amplifier mentioned above, rather than the fabric of the electrical installation. If you were registering one unit per week the load you are looking for would be 1000/(7x24) = 6W, which is typical for a small electronic device that gets mildly warm in use.
Reply to Meter Accuracy - leakage in the UK Electrical Forum area at ElectriciansForums.net
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
hello. I'm using leakage clamp meter to investigate nuisance tripping in my house. It is a MULTICOMP PRO MP780050 that I bought early 2021...