This only applies in the zones (1 and 2). Anywhere else in the bathroom they can be at any height, or they can be mounted immediately outside the door.

Great to know. Per my previous question, is it a violation of any regulation to have the isolator in a different room? I realise it's unorthodox, but curious to understand if it's actually "wrong", if you see what I mean.
 
There isn't a reg that specifically says you can't run three fans from one isolator, but there is a reg that says suitable isolation means shall be provided for maintenance. The problem with not having an isolator is that because many fans are installed in windowless bathrooms, people would be tempted to clean the fan while running (to keep the light on) or run a table lamp on an extension lead etc. The isolator allows the fan to be off for cleaning while the light is on. If your isolator is reasonably close to all the fans I would consider it acceptable to run all three from it, however as suggested by @brianmoooore I would put an additional isolator inline with the MVHR unit located directly adjacent to it, so that it can be serviced while the other two remain active.
 
There isn't a reg that specifically says you can't run three fans from one isolator, but there is a reg that says suitable isolation means shall be provided for maintenance. The problem with not having an isolator is that because many fans are installed in windowless bathrooms, people would be tempted to clean the fan while running (to keep the light on) or run a table lamp on an extension lead etc. The isolator allows the fan to be off for cleaning while the light is on. If your isolator is reasonably close to all the fans I would consider it acceptable to run all three from it, however as suggested by @brianmoooore I would put an additional isolator inline with the MVHR unit located directly adjacent to it, so that it can be serviced while the other two remain active.
Understood.

Many thanks to all three of you for your help, it's much appreciated!
 
  • Like
Reactions: James

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Multiple fans off one isolator
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
aj_london,
Last reply from
aj_london,
Replies
22
Views
6,018

Advert