R

rattlehead85

Located a fault between neutral & earth on a lighting circuit consisting of pvc singles run through steel conduit run between two bedrooms. The point i don't get is the device was an RCBO which apparently has never tripped. I checked the device applying an RCD test which passed and the trip mechanism works fine. Ze value of the installation was good and also the circuit earth continuity was integral.
Any theories as to why this RCBO has not tripped under fault condition present?
 
But what or where was the fault?...where did you find the short?...

Turned out believe it or not that the fault was a twisted bare neutral somebody had joined and pulled through the conduit when the lighting was originally wired!!! The fuseboard had been upgraded last year. Goes to show how much testing was done either pre or post board change that this hadn't been flagged up when it was done.
 
Although that doesn't explain the failure of the RCBO to trip presumably?

Was the conduit definitely earthed?

- - - Updated - - -

Oh sorry you said earth continuity was integral. Ignore me.
 
if the leakage resistance was >8kohms, the RCD would not trip, but your IR test would read 0.00 Mohms.
 

Reply to Neutral-earth fault on lighting circuit with RCBO in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Anyone know of an RCBO manufacturer, apart from Chint,that includes an indicator in the RCBO to indicate if the trip is a earth fault or an overload.
Replies
2
Views
803
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top