Just want to bounch this off others,

1980's house built in rural village, other houses in the village have PME supplies and test out with Ze of around 3.5. Did a quick test when I got there on a ring and getting Zs of 10.45 on further investigation theres no main earth so thought well is this TT if so no rod - can't be - main incomer comes out of the ground looks just like other PME supplies light grey 100A fuse box SWA going in - did the installer just miss the earth off? seems strange - 10mm Main Bonding all there.
 
3.5 is crap for PME anyway. could it be no earth and the reading is from the main bonding to gas and water? is there an earth terminal taken off the cut-out? have you checked in the |CU to see if there is an earth connected ( apart from the bonding)?
 
Last edited:
Thats what I've been thinking - there's no earth to the cut-out the cut-out goes straight to the meter and then to the cu, theres main bonding I didn't get time to test them but I'm assuming gas and water so my thought was I'm getting 10ohms from line to gas or water pipe
 
Thanks everyone,

It's an underground TT -finally found the rod, the earth cable was wrapped in condu and the rod six inches below soil level - 10ohms - great.
 
Don't forget when testing Ze you should have all bonding removed. 10 ohms sounds like you still had gas or water bonds attached and possibly picking up an earth from next door through this.
 
Better go and retest I think.

But picking up on that point then, so this house is TT with earth rod say 70 ohms and next door is say PME with 0.35 ohms, then the first house finds earth through second house rather than the rod?
 

Reply to No earth - is it a TT looks like PME to me in the Australia area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
561
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
664
Morning guys, Just been to look at a CU change and there was a bit of an oddity with the PME connection in the old black cut out. Looking at the...
Replies
2
Views
644
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
717
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock