J.C.E

-
Arms
Reaction score
158
Evening

What ref method would you give t/e running the web of a posi joist?

100mm insulation below the posi joist then a MF and plasterboard ceiling below that

Cable not touch insulation

Cable touching:clipped to posi joist
32A91344-6D4E-4E88-99D3-9555BDD764F6.jpeg
 
Essentially this is to determine the derating factor. I might say 103, although not surrounded by insulation of >100mm the UFH might cause the ambient temperature to be equivalent. Would need to know more about expected UFH temperature for derating first. What is the cable for sockets or lighting? But then if I found out the insulation below the UFH was such that it did not raise the ambient temperature it may be a different conclusion i.e.101. It does need a bit of thinking about from the idea do we use ref. method to derate or ambient temp. to further derate. Meaning a RFC would need to be done in 6mm² or worse, which aint happening. Needs more information I would say.
 
If there is UFH of the floor above, the thermal insulation should be at the top of the joists, keeping the void cool.

Why? Insulation between floors is normally fitted for acoustics rather than any thermal consideration, this is backed up by the specified double layer of acoustic plasterboard. So to achieve the best acoustic performance it would be at the bottom of the void tight against the plasterboard.
 

Reply to Posi joist wiring ref in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi All. I need to extend the cables for a 3 plate ceiling rose/pendant on ground floor ceiling by 450mm. Can I fix the ceiling rose/pendant to...
Replies
5
Views
365
Hi All I wanted to ask a question about the reference method. Passing wiring through holes made at 0.2-0.4 of the joist span. The cables passes...
Replies
1
Views
1K
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
576
hello, i am just about to completely rewire a refurbished house. i have done the same to several houses in the distant past. i have just read...
Replies
6
Views
1K
Hi everyone, I'm hoping someone here can help. I recently did some carpentry work for a new customer and I noticed their electrician had just...
Replies
3
Views
673

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock