Looking for a little help please... running power to workshop.

My home has a 200amp service. Neutral and ground are bonded at meter on outside of home. Main breaker box in house has neutral(white) and ground separated. I have a 100amp breaker installed in the main panel which ran to a sub panel 140 feet from the house. That's where I had a 30 amp breaker for a camper.

Camper is gone and now I have a workshop. Here's my plan and question's.

Wire from 100amp breaker in home is the aluminum 4 wire (2-2-4-6). I plan to remove outdoor sub panels internals and splice the four wires inside the panel... then continue the four wires to the workshop breaker panel.

Panel in workshop is a 100amp with a main 100amp breaker. I plan on green wire to ground bar, black with white stripe to neutral bar, 1 black wire to 100amp breaker.



What to do with final black wire?

Also, will I need ground rods or does house where feed comes from ground it?

Lengthy post but just trying to give as much info as possible.

Thanks for any insight
 
Waste of time. And here's you going 25 efing characters
Looking for a little help please... running power to workshop.

My home has a 200amp service. Neutral and ground are bonded at meter on outside of home. Main breaker box in house has neutral(white) and ground separated. I have a 100amp breaker installed in the main panel which ran to a sub panel 140 feet from the house. That's where I had a 30 amp breaker for a camper.

Camper is gone and now I have a workshop. Here's my plan and question's.

Wire from 100amp breaker in home is the aluminum 4 wire (2-2-4-6). I plan to remove outdoor sub panels internals and splice the four wires inside the panel... then continue the four wires to the workshop breaker panel.

Panel in workshop is a 100amp with a main 100amp breaker. I plan on green wire to ground bar, black with white stripe to neutral bar, 1 black wire to 100amp breaker.



What to do with final black wire?

Also, will I need ground rods or does house where feed comes from ground it?

Lengthy post but just trying to give as much info as possible.

Thanks for any insight
Looking for a little help please... running power to workshop.

My home has a 200amp service. Neutral and ground are bonded at meter on outside of home. Main breaker box in house has neutral(white) and ground separated. I have a 100amp breaker installed in the main panel which ran to a sub panel 140 feet from the house. That's where I had a 30 amp breaker for a camper.

Camper is gone and now I have a workshop. Here's my plan and question's.

Wire from 100amp breaker in home is the aluminum 4 wire (2-2-4-6). I plan to remove outdoor sub panels internals and splice the four wires inside the panel... then continue the four wires to the workshop breaker panel.

Panel in workshop is a 100amp with a main 100amp breaker. I plan on green wire to ground bar, black with white stripe to neutral bar, 1 black wire to 100amp breaker.



What to do with final black wire?

Also, will I need ground rods or does house where feed comes from ground it?

Lengthy post but just trying to give as much info as possible.

Thanks for any insight
this forum is not a waste of time and since you are a do it yourself then all I’m doing to tell you is your extra black wire goes on a double pole breaker. You need to hire an electrician to do this install
 

Reply to Power to workshop from home in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
825
I’m planning on putting in a small (10x10) detached shed for garden storage plus a freezer for meat storage, an in-wall AC unit (for temperature...
Replies
9
Views
1K
I'm starting a new construction single-family residence, I know with the 2020 NEC they require an emergency disconnect on the exterior of the...
Replies
5
Views
2K
I am adding a 60 AMP subpanel for a detached garage/workshop with a 200 foot underground conduit run from the main panel to the sub panel...
Replies
3
Views
879
I have breaker box at least 40 yrs old, both conduit and romex enter box, only one neutral bar that all white wires and bare ground wires attach...
Replies
4
Views
725

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock