Hi ,

Could someone answer the following for me? i don't have reg book handy and when i google i'm getting mixed answers.

1. maximum disconnection time for a type A rcd on a consumer unit at times 1 setting?

2. on a ring continuity test the readings i measured and put on cert were L-L 0.36 N-N 0.29. I have been told this is unacceptable as the difference can't be more that 0.05 ohms between L-L and N-N. Is this correct and if so where would i find this in the regs or onsite guide?


Thanks
 
1. Assuming it is 61009 or 61008 then 300ms.
2. I don't believe there is a requirement stating this but morevrule of thumb. Your readings do warrant some investigation.
 
The 0.05 ohms comes from the OSG, I have not seen it in the regs book. Certainly if the readings obtained were for intial verification tests as suggested by the thread title they would not be acceptable, I would not be overly concerned however if these readings were on an existing circuit as part of an EICR.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
glasgow

Thread Information

Title
questions for installation cert
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
thomaspotato,
Last reply from
OLDBOY,
Replies
2
Views
853

Advert