Simple job to add an extra socket to top floor 'rfc'. Top floor was converted some 8-10 years ago but no certs available. Took Zs from socket I was going to spur from which was .6ish Ohm, turned off supply, proved dead then took end to end readings (at socket I intended to spur from) to prove ring and all fine. Realised that ring cable (2.5mm) passed directly behind proposed new socket position so went down to cu to disconnect circuit before cutting cable to find that the mcb was feeding 1 x 6mm t & e. Spoke to owners who said that this cable had been upgraded during the conversion and feeds a jb at bottom of flight of stairs to top floor. They assure me this was done by an electrician.Whilst I haven't lifted carpets as they never go back the same, it does check out.
Therefore I have a ring beginning and ending at an 'accessible' jb which is fed from cu by 6mm t&e which does not comply with app 15 which is headed 'informative', so a radial ring combination. Making it a true ring as defined in App 15 is impractical due to floor tiles above lath and plaster ceiling. Load wise the ring could be broken and mcb downrated to 20A but this will actually increase the earth path resistance albeit still well within disconnection times. Mem board.
Arguments against leaving this as is please and how to describe circuit on cert
Therefore I have a ring beginning and ending at an 'accessible' jb which is fed from cu by 6mm t&e which does not comply with app 15 which is headed 'informative', so a radial ring combination. Making it a true ring as defined in App 15 is impractical due to floor tiles above lath and plaster ceiling. Load wise the ring could be broken and mcb downrated to 20A but this will actually increase the earth path resistance albeit still well within disconnection times. Mem board.
Arguments against leaving this as is please and how to describe circuit on cert