hi can some one clarify how to rcd test a rcbo on a lighting circuit, do i test at a light and do i conect to l+n+e or is it better to test at c u. if so do i connect crock to earth bar or earth flex on rcbo then put probes on nuteral on rcbo and outgoing live ?
 
You can test at a light or at the load terminals of the RCBO. Connect L-N-E probes to L-N-E !! at whatever terminals youi are testing at. Testing at a light can give extended trip times due to loads in circuit,so it is often better to test the RCBO at the load terminals with outgoing circuit disconnected.

Some RCBO's have an issue where they wont respond to a test directly connected to the load terminals....in that case connect short tails and test on them.
 
hi can some one clarify how to rcd test a rcbo on a lighting circuit, do i test at a light and do i conect to l+n+e or is it better to test at c u. if so do i connect crock to earth bar or earth flex on rcbo then put probes on nuteral on rcbo and outgoing live ?

I think if the job is to test the RCBO, then that's what you test.
 
You can test at a light or at the load terminals of the RCBO. Connect L-N-E probes to L-N-E !! at whatever terminals youi are testing at. Testing at a light can give extended trip times due to loads in circuit,so it is often better to test the RCBO at the load terminals with outgoing circuit disconnected.

Some RCBO's have an issue where they wont respond to a test directly connected to the load terminals....in that case connect short tails and test on them.

ok thanks for the help so just to confirm conect to earth wire on rcbo and put tails in live an nuteral just incase there is a issue with direct contact
 
ok thanks for that so just to confirm i can connect to earth wire on rcbo and put tails in l+n load side to resolve any rcbo issues with direct contact
 
Was going to ask a similar question. Done my 2392, read myOSG & GSN 3 and watched a vid from the ‘learning lounge’ on the same subject.

I’m kind of confused about breaching EWR on live testing. Onan earth loop test on final radial circuits (i.e. lighting), it’s recommended to carry out the calculation method for Zs (=Ze+(R1+R2)), so as not to breach EWR.
However, to do a RCD test on a RCBO radial (i.e. live test),you could only do that at a lighting point, exposing live parts or at the CU (only testing the device), but again with the cover removed and live parts exposed?

As regards IR testing of a RCBO, I see some manufactures state their RCBO can withstand IR testing, but can give false readings, so should be disconnected? I've seen other instructions to disconnect the ‘earthfly lead’ and test each circuit (with RCBO turned off) independently.

Being picky I know, but having my assessment soon, so I want to do it correctly.

Apologies paddyscouse for hyjacking your thread, but think it is asking the same question.
 
Was going to ask a similar question. Done my 2392, read myOSG & GSN 3 and watched a vid from the ‘learning lounge’ on the same subject.

I’m kind of confused about breaching EWR on live testing. Onan earth loop test on final radial circuits (i.e. lighting), it’s recommended to carry out the calculation method for Zs (=Ze+(R1+R2)), so as not to breach EWR.
However, to do a RCD test on a RCBO radial (i.e. live test),you could only do that at a lighting point, exposing live parts or at the CU (only testing the device), but again with the cover removed and live parts exposed?

As regards IR testing of a RCBO, I see some manufactures state their RCBO can withstand IR testing, but can give false readings, so should be disconnected? I've seen other instructions to disconnect the ‘earthfly lead’ and test each circuit (with RCBO turned off) independently.

Being picky I know, but having my assessment soon, so I want to do it correctly.

Apologies paddyscouse for hyjacking your thread, but think it is asking the same question.

Disconnect circuit from RCBO for an IR test.
Live testing is an essential part of testing.Provided you are using correct meters and leads designed for live testing and follow obvious safety proceedures .....crack on.
 
hi guys i need to ask this, im due an eic assesment soon on a c u (rcbo board) and i need to be sure about rcd testing on all circuits (not sockets) so if im to do a rcd test at board do i connect to the nuteral flex on rcbo or to the terminal or do i put a tail in ,do connect to earth flex on rcbo or terminal bar, do i connect to live terminal or put a tail in, reason i mention tails is some one told me you may get no trip issues with direct contact to terminals can some one explain in laymans terms in detail on the best wat to do this test .....apreciated
 
hi can some one clarify how to rcd test a rcbo on a lighting circuit, do i test at a light and do i conect to l+n+e or is it better to test at c u. if so do i connect crock to earth bar or earth flex on rcbo then put probes on nuteral on rcbo and outgoing live ?
What sort of test equipment have you got, My advice if you have one of the latest 17th testers would be to temp conect a 13a SSO to a suitable point of the lighting circuit and do the test as you would on a SSO circuit Simples
 
What sort of test equipment have you got, My advice if you have one of the latest 17th testers would be to temp conect a 13a SSO to a suitable point of the lighting circuit and do the test as you would on a SSO circuit Simples

Strange that, seeing as virtually all the manufactures all state testing at the RCD units terminals!! Nothing wrong with testing down stream, but not for any official/recorded testing!! As has been already stated your testing the RCD unit, not the circuit it's connected as well!!

Are you sure your not getting confused with ELI testing.... lol!!
 
Strange that, seeing as virtually all the manufactures all state testing at the RCD units terminals!! Nothing wrong with testing down stream, but not for any official/recorded testing!! As has been already stated your testing the RCD unit, not the circuit it's connected as well!!

Are you sure your not getting confused with ELI testing.... lol!!

Exactly-the reason for testing at the terminals of the device is that any capacitance in the circuit (ballasts etc.) while not affecting the actual disconnection time, affect the displayed disconnection time on the test instrument.
 

Reply to rcbo testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Just wondering if someone could help provide an explanation as to why this might be the case when testing an RCBO. Testing the RCBO at the DB...
Replies
7
Views
310
Just to be clear… I am going to do the correct thing here and pay for the correct parts…. I just wanted to start the discussion. My particular...
Replies
6
Views
313
Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
832
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
522
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
779

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock