OK we are told RCBOs are the way to go.
Agreed.
Because this will do away with using a RCD but, and I guess this has been questioned and possibly answered before, why buy an RCBO that only protects phase side (single pole RCBO) of the cct?
Have I missed something?
Do we put in one RCD!?
Fred
 
If you're that worried, use SP+N RCBO's that are becoming increasingly available!!

SP RCBO's are not as bad as some make them out to be, we have been using them for a good number of years now, (without any major safety concerns being reported) and SP MCB's and fuses for a damn sight longer!!
 
double pole RCBOs or single pole with switched N are the best way, but cost is a factor.
 
OK we are told RCBOs are the way to go.
Agreed.
Because this will do away with using a RCD but, and I guess this has been questioned and possibly answered before, why buy an RCBO that only protects phase side (single pole RCBO) of the cct?
Have I missed something?
Do we put in one RCD!?
Fred

It's the phase side that bites,thats why.
 
If you're that worried, use SP+N RCBO's that are becoming increasingly available!!

SP RCBO's are not as bad as some make them out to be, we have been using them for a good number of years now, (without any major safety concerns being reported) and SP MCB's and fuses for a damn sight longer!!

You’ve changed your tune.

The trouble is the SP RCBO just don’t match what it says on the tin. For this reason I think many have accepted them as an instant cure all in every situation. This can only be attributed to lack of knowledge on the part of the electrician. (The ones that bite my head off now will be the ones in the know.)

Some manufacturers do point out the short comings of the SP RCBO in handling a N→E fault. To my mind it should be made clear to everyone. As we’ve often discussed it seems to be the doctrine of colleges to preach fitting RCD’s to everything.
 
You’ve changed your tune.

The trouble is the SP RCBO just don’t match what it says on the tin. For this reason I think many have accepted them as an instant cure all in every situation. This can only be attributed to lack of knowledge on the part of the electrician. (The ones that bite my head off now will be the ones in the know.)

Some manufacturers do point out the short comings of the SP RCBO in handling a N→E fault. To my mind it should be made clear to everyone. As we’ve often discussed it seems to be the doctrine of colleges to preach fitting RCD’s to everything.

A single pole MCB wont react to a N-E fault. To my mind the RCD element of an RCBO on a TN system is likely to be additional protection only,not fault protection.
 
A single pole MCB wont react to a N-E fault. To my mind the RCD element of an RCBO on a TN system is likely to be additional protection only,not fault protection.

An mcb is not designed to react to N-E faults so there is no issue there.
It reacts to L-L, L-N or L-E faults by disconnecting the L or Ls

A SP RCBO does react to N-E faults, but the way it reacts is to disconnect the L which has no fault in it.
This is the problem.
 
An mcb is not designed to react to N-E faults so there is no issue there.
It reacts to L-L, L-N or L-E faults by disconnecting the L or Ls

A SP RCBO does react to N-E faults, but the way it reacts is to disconnect the L which has no fault in it.
This is the problem.

None of which really matters if the RCBO is simply used as an MCB with additional protection.
 
None of which really matters if the RCBO is simply used as an MCB with additional protection.

What on earth are you talking about?

If an mcb is needed you use it as an mcb.

If RCD protection is needed in addition you either install an RCCB before or after the mcb or an RCBO to provide both functions in one.

Whatever reason you install an RCBO for then if it is SP it will detect N-E faults and not disconnect them, it will disconnect the L.
 
Is disconnecting the L on a N-E fault a problem?

It's completely pointless, you might as well have a device which switches the gas off when the water main bursts!

It could also give a false sense of security as someone might assume that since a protective device has operated whatever fault is present will have been disconnected and so not worry about investigating in a hurry. But a N-E fault will still be connected which could present a massive fire risk through diverted neutral currents
 

Reply to RCBOs vs RCDs Pt2 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

We have a customer in a large office block with all power in the building fed from an Electrak plug in busbar system. Lots of desks, lots of...
Replies
7
Views
547
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
731
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
914
Evening all, I have a little conundrum I need to get resolved. I’ve moved an EV charger from a single phase board that was on a 40a breaker and...
Replies
9
Views
552

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock