OCPD is overcurrent protective device. Also known as a fuse or circuit breaker.
So if I have read this right you have a 16mm SWA connected directly to the meter, then jointed to a bit of 16mm T&E which then continues to the CU??
You have broken many regulations if this is the case!
There cannot be more than 3mtrs of conductor between the meter and the first bit of switchgear whether that is the CU or a switchfuse to feed a submain.
The cpc in T&E is not big enough for a main bond so is undersized to feed the CU
What have you fitted the SWA gland to at the meter end and how have you earthed the armour?