OCPD is overcurrent protective device. Also known as a fuse or circuit breaker.

So if I have read this right you have a 16mm SWA connected directly to the meter, then jointed to a bit of 16mm T&E which then continues to the CU??

You have broken many regulations if this is the case!
There cannot be more than 3mtrs of conductor between the meter and the first bit of switchgear whether that is the CU or a switchfuse to feed a submain.

The cpc in T&E is not big enough for a main bond so is undersized to feed the CU

What have you fitted the SWA gland to at the meter end and how have you earthed the armour?
 
what i meant was due to old consumer unit being moved due to new kitchen.

I ran 16mm pvc from mains income cupboard outside through wall which came out in 2 zones, it went up wall 50 mm deep in capping vertically behind cooker hood run.

Then it was about a metre then into loft across then down trunking to new board the 16mm was in zone with skt outlet to plug in hood which would be behind the vertical vent cover.

The people doing the kitchen knew it was there agreed to use grease filters, and not vent outside as vent would be higher than the skt for hood, they after id gone dug out ring main for hood, along with 16mm cut a 2 brick hole for vent, leaving no where for cables to go.

They then cut mains thinking it was cooker cable, with the intention of reconnecting themselves when it went bang, i got blame so as to try to help, i had no choice to but to go in swa outside upto loft height then back in and swapped back to 16mm pvc they now are saying this is wrong i believe I've done it correctly as it was in first place

Its still written by a 7 year old!
 
Just imagine being a customer and getting a quote from this dude!!! Combo of txt speak, bad grammar, and no punctuation. Seriously how would you ever get any work if this is the quality of your communication? it's a riddle within an enigma.....or a google translation from Swahili!!!
 

Reply to rcd protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
752
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
554
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
854
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
808
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock